400.8(5) excludes them from being used above suspended or dropped ceilings regardless the reason. ,..
Appliances where the fastening means and mechanical connections
are specifically designed to permit ready removal for maintenance and
repair, and the appliance is intended or identified for flexible cord
connection
220/221 said:Heh heh...no.
It doen't say "regardless of the reason" it says "Unless specifically permitted in 400.7" which it is...
Again...not tryin to be difficult, only to learn. Sometimes I get something stuck in my head and I miss the obvious.
edit. I can't tell what is plugged in (in the image). I think it matters.
I still don't see any thing about dropped or suspended ceilings ?? I was taught 400.8 modifies 400.7Quote:
Appliances where the fastening means and mechanical connections
are specifically designed to permit ready removal for maintenance and
repair, and the appliance is intended or identified for flexible cord
connection
Quote:
Appliances where the fastening means and mechanical connections
are specifically designed to permit ready removal for maintenance and
repair, and the appliance is intended or identified for flexible cord
connection
220/221 said:edit. I can't tell what is plugged in (in the image). I think it matters.
220/221 said:It doen't say "regardless of the reason" it says "Unless specifically permitted in 400.7" which it is...
Show me where in 400.7 it specifically permits a flexible cord on an appliance to be installed above a suspended ceiling.
400.7 Uses Permitted
(A) Uses Flexible cords and cables shall be used only for the following:
(6)Connection of utilization equipment to facilitate frequent interchange
(8)Appliances where the fastening means and mechanical connections
are specifically designed to permit ready removal for maintenance and
repair, and the appliance is intended or identified for flexible cord
connection
400.8 Uses Not Permitted
Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following:
(5)Where concealed by walls, floors, or ceilings or located above
suspended or dropped ceilings
400.7 Uses Permitted.
(A) Uses. Flexible cords and cables shall be used only for
the following:
...
(2) Wiring of luminaires (fixtures)
...
400.8 Uses Not Permitted. Unless specifically permitted
in 400.7, flexible cords and cables shall not be used for the
following:
...
(5) Where concealed by walls, floors, or ceilings or located
above suspended or dropped ceilings
...
petersonra said:Does this not strongly suggest that one could wire drop in light fixtures with cord in drop ceilings?
So IYO would it be O.K. to run the cord through a hole in the ceiling ?? or through a doorway as long as it were to serve ;
220/221 said:No....but I think that's another issue.
How you would explain this ??
220/221 said:I am having a hard enough time focusing on the original post. Don't get chasing after something else.:smile:
And looking ONLY at 400.7 and 400.8, I still say it is OK.
If one section says yes and the other says no....which is right?
And looking ONLY at 400.7 and 400.8, I still say it is OK.
If one section says yes and the other says no....which is right?In order to satisfy the "specifically permitted" part of 400.8, the words "above ceilings" would have to appear in 400.7. There are general permissions in 400.7, but there is not a "specific permission" to install a code above a ceiling.
Don http://forums.mikeholt.com/editpost.php?do=editpost&p=749193
In order to satisfy the "specifically permitted" part of 400.8, the words "above ceilings" would have to appear in 400.7.
There are general permissions in 400.7, but there is not a "specific permission" to install a code above a ceiling.
There is not specific permission regarding ANYTHING above a ceiling in 400.7
so the first line of 400.8 is irrelevant?
220/221 said:There is NOTHING in 7 that refers to ceilings so what is 8 referring to?