Outlets above suspended ceiling.

Status
Not open for further replies.

cschmid

Senior Member
No one here see an issue that is going on regularly..So what do you think the solution should be..I believe it should be that the manufacturer should have there equipment with fixture whips instead of cords..or have the code worded to allow CCTV and other such items to be cord connected..Maybe we can come up with a meaningful proposal here..
 
cschmid said:
In order for a flexible cord to deteriorate like that it would have to be a permanent installation because of the time it takes to deteriorate..CCTV's are not permanent installations..so why is it okay to run a drill from outlets in a recessed ceiling but not okay to run a CCTV..neither are permanent installations and both require frequent servicing..


What is your determining factor to say the CCTV camera installations are not permanent?
The drill is used for work and then unplugged. Are you saying that the cameras are installed just for a days work and then unplugged?
 
cschmid said:
No one here see an issue that is going on regularly..So what do you think the solution should be..I believe it should be that the manufacturer should have there equipment with fixture whips instead of cords..or have the code worded to allow CCTV and other such items to be cord connected..Maybe we can come up with a meaningful proposal here..

Some do, you would have to order it that way. I know that most cameras and HVAC equipment is purchased by other than electricians. The issue should probably be dealt with through the purchaser.
 

iwire

Moderator
Staff member
Location
Massachusetts
cschmid said:
In order for a flexible cord to deteriorate like that it would have to be a permanent installation because of the time it takes to deteriorate..CCTV's are not permanent installations....

For that matter nothing is permanent. :smile:

But it is my opinion that once you secure something (like a Camera, monitor or vid projector) to the building it is much less temporary then a drill.
 

cschmid

Senior Member
I guess since we are on this subject I want to learn something..I have found the camera's we have looked at are all cord connected..So How do you guys deal with this..I am not trying to be against the code I just want to understand and find how to do it correctly if I am doing it wrong..
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Well per 400.8 it is wrong.

You could mount the receptacle flush and plug it in below the ceiling or use a whip.

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Our security division will not use cameras that will not meet a code compliant installation.

We use cameras that utilize 24 v power supplies, wiring methods, and cables approved for the application, (as in Plenum rated or what have you) so a camera that can not be installed per applicable codes is not an exception to a proper installation.

I guarantee a manufacturer will have a code compliant solution if they are about to loose a large sale.

Roger
 
The power supply shown in the all-cctv.com link is permissable, even plugged in within the ceiling.
Power cords are not permitted.

I inspect a lot of the CCTV and other instances where the installation is within drop ceilings, either of two installs occur.
1. the install is code compliant based on Art 400, or
2. they are changing the original install to make it code compliant. I have yet had a contractor not be able to find a way to make it work.
 

cschmid

Senior Member
Pierre C Belarge said:
The power supply shown in the all-cctv.com link is permissable, even plugged in within the ceiling.
Power cords are not permitted.

LMAO

Them are what I am using for our cameras and video display screens..gotta run but will be back..Thank you I have learned something
 

220/221

Senior Member
Location
AZ
We use cameras that utilize 24 v power supplies, wiring methods, and cables approved for the application, (as in Plenum rated or what have you) so a camera that can not be installed per applicable codes is not an exception to a proper installation.



Apparently you can't plug the transformers in either....right?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
220/221 said:
Apparently you can't plug the transformers in either....right?

Are the transformers connected to flexible cord?

The prohibition is for flexible cord installed above a suspended ceiling, not LV transformers, unless they are connected to flexible cord.

Chris
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
220/221 said:
Apparently you can't plug the transformers in either....right?

As Chris stated, the transformers are fine, flexible cords are what is not allowed.

Roger
 

cschmid

Senior Member
So since the transformer plugs directly into the outlet it is not cord connected and the 24 volts power connection is not classified as a cord connection..interesting..so if there is a 12 inch cord between transformer and the plug and it is all factory made is that still legal or is it classified as a power cord? since the definition of power cord is a cord carrying 120 volts or more..or do we have a different definition for power cord??I thought the code state flexible cords not power cords..I will like it when my code on CD ROM gets here so it is easier to cut and paste..
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I thought the code state flexible cords not power cords..

It does, if the transformer is connect to any flexible cord of the types listed in Table 400.4 regardless of the voltage within the flexible cord, then it is a violation.

Chris
 

220/221

Senior Member
Location
AZ
I read mis read this. I missed the connected to the branch circuit.


600.21 Ballasts, Transformers, and Electronic Power Supplies

(F) Suspended Ceilings. Ballasts, transformers, and electronic power supplies are permitted to be located above suspended ceilings, provided their enclosures are securely fastened in place and not dependent on the suspended ceiling grid for support. Ballasts, transformers, and electronic power supplies installed in suspended ceilings cannot be connected to the branch circuit by flexible cord.



After the transformer that is plugged directly into the outlet (no flex cord) the LV wire is no longer part of the branch circuit and is allowable....right?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
220/221 said:
I read mis read this. I missed the connected to the branch circuit.






After the transformer that is plugged directly into the outlet (no flex cord) the LV wire is no longer part of the branch circuit and is allowable....right?

Again, the prohibition is the installation of flexible cord above a suspended ceiling regardless of the voltage of the system utilizing the flexible cord.

Chris
 