Outlets above suspended ceiling.

Status
Not open for further replies.

220/221

Senior Member
Location
AZ
Again, the prohibition is the installation of flexible cord above a suspended ceiling regardless of the voltage of the system utilizing the flexible cord


Wouldn't that make speaker wire illegal?
Alarm wire?
Is cord different from cable?

Dumb questions I'm sure. Just trying to understand completely.

Is it flexible cord coming off the cube style transformer plugged into the outlet (cell phone style)?
 

realolman

Senior Member

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
220/221 said:
Wouldn't that make speaker wire illegal?
Alarm wire?
Is cord different from cable?

Dumb questions I'm sure. Just trying to understand completely.

Is it flexible cord coming off the cube style transformer plugged into the outlet (cell phone style)?

If the speaker wire being used is a flexible cord listed in Table 400.4 then it is illegal.

We do not have to look at 400.7 and 400.8 for other types of cables covered in other articles such as 720 and 725 for examples.

Roger
 
roger said:
Realolman, notice the power supply plugs directly into the receptacle, after this the low voltage side is not using a flexible cord listed in 400.4


Roger


This is one of the keys to this topic.

Notice in the link I mentioned, that a small transformer is plugged into the receptacle and the cable that is on the load side of the transformer is not one listed in Table 400.4.
 

cschmid

Senior Member
so now if the transformer has a flexible cord 12" before the actual transformer it is not allowed..but the transformer that plugs into the outlet is allowed..I believe we might be close to the answer for the original question now..

mfbettwy said:
is it permissable to install a 120v /20amp duplex receptacle above a suspended ceiling. this outlet would serve a plug in power supply for a CCTV camera/

Yes you can..
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
cschmid said:
so now if the transformer has a flexible cord 12" before the actual transformer it is not allowed..but the transformer that plugs into the outlet is allowed..I believe we might be close to the answer for the original question now..



Yes you can..

You should have read the first reply.

Roger
 

M. D.

Senior Member
Wouldn't the class 2 transformer have to meet;

UL 2043 - Fire Test for Heat and Visible Smoke Release for Discrete Products and Their Accessories Installed in Air-Handling Spaces: Determine the rate of heat release and the rate of smoke release of the burning product samples as they relate to the requirements for fire-resistant and low-smoke-producing characteristics for discrete products (electrical equipment) intended to be installed in air handling spaces such as above suspended ceiling.

Are we assuming that it does or is this an inhierent part of the standard for these power supplies?
 

iwire

Moderator
Staff member
Location
Massachusetts
M. D. said:
Wouldn't the class 2 transformer have to meet;

LMAO.....:D just when it appeared this thread had reached a conclusion.

I think your right if it is an air handling space.

300.22(C)(2)
 

realolman

Senior Member
Re: the transformer for the cctv camera, what type cord is it?

I understand that the restriction against using flexible cords above a suspended ceiling is a part of the NEC.

I also think that the fact that this topic has gone this length and come down to such hair splitting indicates that many feel it is an unreasonable restriction.

It seems to me a greater risk of injury to make thousands of people stand on step ladders up inside suspended ceilings to wire and un-wire fixtures rather than unplug them, than would ever occur from having them plugged in with a flexible cord.

Everything deteriorates.
No one makes a flexible cord that is capable of withstanding the environment above a suspended ceiling, and deteriorates at a similar rate to the things that ARE permitted to be there?
 
Last edited:

cschmid

Senior Member
yes rodger raider answered correctly in post #2 but the real discussion is what can the outlet be used for..The OP wanted to plug in a transformer for a CCTV now MD has to throw in this smoke hazard info..So my question is how would we tell if it qualifies to be above the suspended ceiling with UL203??

LOL Good morning everyone..
 

M. D.

Senior Member
Oh no ,.. you don't get to pin that on me I didn't write it I just read it and then TRY to understand it.:)

What did you guys think I was talking about in post # 72 ,???

And I don't think it is over restrictive ,... smoke kills more people than the heat of the flames.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Cschmud,

cschmid said:
yes rodger raider answered correctly in post #2 but the real discussion is what can the outlet be used for..
It can be used for many things, use your imagination. You can't use it for a flexible cord prohibited in 400.8



cschmid said:
The OP wanted to plug in a transformer for a CCTV now MD has to throw in this smoke hazard info..So my question is how would we tell if it qualifies to be above the suspended ceiling with UL203??
Simple, check the listing information.

If you are going to use a item in a plenum ceiling, it and everything associated with it will need to suitable for the installation, note what I said in post #69.


Now let me clarify my position, I think there should be some exceptions to the rules in 400.8 but there are not, so, if you try to use a cord above a ceiling an inspector should tag it or give you "special permission in writing" (good luck getting it)

You can install a receptacle in a ceiling for service use, but you can't leave a cord plugged in to it, you can also install a panel in a residential bath room but you can't put breakers in it, that's just the way it is.

Roger
 
Last edited:

cschmid

Senior Member
MD I did not say it was your fault but you did quote the rule and I agree smoke is more dangerous than allot of things..Rodger I do understand yet we need to understand the equipment that gets used in the outlets above suspended ceilings..they are not service outlets as no one knows they are there unless you installed them..so does the label on the plug in transformer have to state it is for above suspended ceilings or are we to assume if it is UL listed it is good to go..must go finish rough in..have good day..
 

iwire

Moderator
Staff member
Location
Massachusetts
The transformer would have to be listed for use in handling spaces if in fact the ceiling space was being used for air handling, not all are.

I don't think we can assume all (or any) of these plug in transformers are listed for that.

The fact that it is common to see many items plugged in above a ceiling has absolutely nothing to do with what the code actually allows or prohibits.
 

M. D.

Senior Member
cschmid said:
MD I did not say it was your fault but you did quote the rule and I agree smoke is more dangerous than allot of things

I was just joking around,.. I know , you know, it is not my fault:smile:
 