jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Yes I am adamant about it. While a crawl may be damp, the NEC does not call it damp nor do I see that I can call it damp. There is no standard, like a % of moisture, for me to use.
yet somehow you have used that standard for under the siding. How many homes have tin roofs with nm cable run in the 3/4" sleepers. Is that outside the house? If the nm is attached to the joist in the attic close to the shingles is that outside the house? It seems siding and roofing is not that different but you are choosing that one is outside but not the other. IMO, you are totally inconsistent.

The nec does not call a crawl damp -- Why? because it normally is not wet or damp there. That is bull-- there is always moisture in a crawl space except for these new sealed crawls. I have been there with water dripping from the joist from condensation.

I guess the def. of dry location doesn't work under the siding. Do you really think this is a passageway for water and moisture? There will be more moisture at the dew point--

Siding is an exterior covering (Chapter 7 of The Residential Code). It is applied to the outside of the structure. 334 NEC does not allow NM outside.
Roofing is an exterior covering but the inside of the roof is not outside. :-?

I am sorry your logic seems to be totally inconsistent and outside the scope of the NEC, IMO. I guess we will have to agree to disagree. :)
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
yet somehow you have used that standard for under the siding. How many homes have tin roofs with nm cable run in the 3/4" sleepers. Is that outside the house? If the nm is attached to the joist in the attic close to the shingles is that outside the house? It seems siding and roofing is not that different but you are choosing that one is outside but not the other. IMO, you are totally inconsistent.

The nec does not call a crawl damp -- Why? because it normally is not wet or damp there. That is bull-- there is always moisture in a crawl space except for these new sealed crawls. I have been there with water dripping from the joist from condensation.

I guess the def. of dry location doesn't work under the siding. Do you really think this is a passageway for water and moisture? There will be more moisture at the dew point--

Roofing is an exterior covering but the inside of the roof is not outside. :-?

I am sorry your logic seems to be totally inconsistent and outside the scope of the NEC, IMO. I guess we will have to agree to disagree. :)

The attic is a dry location. No it is not outside. You do not staple NM to the outside of the sheathing there either.

You are correct dry location does not apply to the area under the siding.

The building industry makes the rules not me.

http://www.awc.org/pdf/wcd1-300.pdf

Go to PP 41 and look at figs. 49 & 50. The building paper is there to protect the sheathing, keeping it dry! So why do you think that installing NM over it is code compliant?
 

ike5547

Senior Member
Location
Chico, CA
Occupation
Electrician

Those are nice, but are not a requirement, as far as I know.



OK. It says 334.12(A)(1) In any dwelling or structure not specifically permitted in 334.10(1), (2), and (3).

Where is it permitted to be outside?

We are now required to prove a negative, or an un-negative, as the case may be when discussing the code? If it is not expressly permitted, it is prohibited by default?

Where is NM specifically permitted to be in crawl spaces?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
We are now required to prove a negative, or an un-negative, as the case may be when discussing the code? If it is not expressly permitted, it is prohibited by default?

I disagree, generally it the converse. If it is not prohibited then it is permitted.
 

ike5547

Senior Member
Location
Chico, CA
Occupation
Electrician
The argument seems to hinge on the felt paper.

To me, there seems that there is a reason for the conscious inclusion of the word 'excessive' in 334.12(B)(4). Wood vs. NM require differing degrees of protection and don't merit identical treatment in this regard. I believe this argument against NM under siding is extremely tenuous and you've gone far, far out of your way to cobble it together.

I, also, agree to disagree until a truly authoritative source says otherwise.
 

ike5547

Senior Member
Location
Chico, CA
Occupation
Electrician
Would you install Type AC behind the siding?


That's an interesting question. No, I wouldn't, based on what I've learned here today. And I don't think I would have before today, either. The uses not permitted state "damp locations."

I've never even considered it before. I'd have to think more about it. No, I wouldn't -- for personal reasons if nothing else.

Would you allow it under a crawl space?
 
Last edited:

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
That's an interesting question. No, I wouldn't, based on what I've learned here today. And I don't think I would have before today, either. The uses not permitted state "damp locations."

I've never even considered it before. I'd have to think more about it. No, I wouldn't -- for personal reasons if nothing else.

Would you allow it under a crawl space?

I see nothing that would prohibit it.
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
Neither do I.

And I'm interested to hear other opinions on the type AC thing. You seem to have a strong point there.

Hold on. I've changed my mind on this area being 'outside'. If it was outside you would be able to install service conductors under it.

I still believe it to be a damp location.
 

glene77is

Senior Member
Location
Memphis, TN
Do I understand this correctly (can't quote the code right now)
that Rommex if installed on an exterior wall with furring strip
needs to be protected either by conduit or a plate?

(Originally posted by) Strife,

Please explain your posted question more fully.

Maybe make a little diagram. :)
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Hold on. I've changed my mind on this area being 'outside'. If it was outside you would be able to install service conductors under it.

I still believe it to be a damp location.

Mike this is exactly what I was saying earlier. You have the building code that you adamantly stood behind now that you don't like the way it fits in the NEC you change your mind. You can't just take pieces-- if the building code is your bible then you must allow se cable under the siding but instead you decide that it doesn't work so well in a more important situation so you change your thinking. The code still says what it says. You are totally inconsistent and make the codes fit your view. That , IMO, is not a good way to inspect.

Also, the area under the siding fits very nicely with the definition of dry location but you will not honor that because you are stuck in your thinking. I am sorry if I sound harsh- I tried to word it so that it wasn't harsh but I feel honesty is important also--
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
Mike this is exactly what I was saying earlier. You have the building code that you adamantly stood behind now that you don't like the way it fits in the NEC you change your mind. You can't just take pieces-- if the building code is your bible then you must allow se cable under the siding but instead you decide that it doesn't work so well in a more important situation so you change your thinking. The code still says what it says. You are totally inconsistent and make the codes fit your view. That , IMO, is not a good way to inspect.

Also, the area under the siding fits very nicely with the definition of dry location but you will not honor that because you are stuck in your thinking. I am sorry if I sound harsh- I tried to word it so that it wasn't harsh but I feel honesty is important also--

Before I thought I was right now I know I am. I consider the area damp because of the information that I posted earlier.

How I inspect is much different than how we discuss things here.
 

pete m.

Senior Member
Location
Ohio
Since this thread is "splitting hairs"...

Would anyone consider the interior of a NEMA 3R disconnect to be a "damp location"?

The reason for the question is that typically the NM cable passes from the interior of the structure through vapor barriers, siding, brick, etc.. and into the back of the disconnect that may serve the condensing unit.

If it is determined that NM cable cannot be used outside then how is it that it is able to be utilized for the purpose stated above?

Pete
 

Jim W in Tampa

Senior Member
Location
Tampa Florida
Since this thread is "splitting hairs"...

Would anyone consider the interior of a NEMA 3R disconnect to be a "damp location"?

The reason for the question is that typically the NM cable passes from the interior of the structure through vapor barriers, siding, brick, etc.. and into the back of the disconnect that may serve the condensing unit.

If it is determined that NM cable cannot be used outside then how is it that it is able to be utilized for the purpose stated above?

Pete

You just had to open up that can of worms LOL
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I think nm cable should be listed for damp location. I cannot understand why it isn't. Like I said, there are thousands of crawl spaces I would consider damp.
 