Existing : at most 2.3 amps of fluorescent load at 120V, 12AWG protected by 20A circuit with a SPST toggle switch.
1) Is it permissable to install a switch rated 6 amp, 120V in place of the toggle switch?
2) If yes, what if the 6 amp switch includes 18AWG leads?? The owner desires a pull-chain switch and manufacturers of such have 18AWG leads standard. Would this violate conductor branch circuit overcurrent protection? I doubt it would make much difference if it had 12AWG leads.
http://www.hubbellcatalog.com/raco/images/RACO/Specialty Switches/PDF/D2.pdf
My gut feeling is that this would be unacceptable since these devices are made for appliances, but can't seem to quite put my finger on it.
Thoughts?