Someone in another forum questioned the conductor size (#2) on the shorting circuit that goes to the 3rd contact, connected to 1, 2 &3. the contactor is supposed to be sized for a minimum of 50% of the current rating of the other contactors, because it is the Y point for half of the circuit (in high speed, it is two parallel Y winding sets, one set is already connected, the contactor connects the others). So with the FLA rating of the motor requiring 500MCM cable, the shorting circuit conductors should have been a minimum of 3/0, maybe 4/0 with VD. My thought is that someone erroneously sized those conductors for the Low Speed current, but in Low, those conductors don't even carry current. So what I think is happening is that the under sized conductors are creating a VD in that half of the 2Y windings, evidenced by the fact that the two sets of windings are not showing the same current, and they should be.
This is my take as well. Conductors a should be sized for half of the FLA, as well as the contactor for the second half of the winding.
As evidenced by the OP first post.
High speed shorted connection current to problem fan motor:
T1 - 161.9A
T2 - 154A
T3 - 156.6A
High speed shorted connection current to other normally operating fan motor:
T1 - 135.5A
T2 - 136.6A
T3 - 139.4A
The Low speed and High speed shorted conductors are a sun resistant direct burial 90C 600V, three conductor and ground 2AWG jacketed cable. When this motor is operating in high speed the three conductor cable is showing very warm with our IR camera, naturally since it has about 30A higher flow than the 2AWG is rated for. I have found some cracked insulation on the individual 2AWG conductors in the motor junction box and sealed these up with silicone high voltage tape and super 33.
Some major voltage drop going on here, causing the other half of the winding to pick up the slack. Roasting cables and bearings in the process. Should be pretty simple to compare wire sizes and contactors between fans.
Also is good to note that there are three types of 2S1W motor types, and the one in use here is the variable torque. Low speed horsepower is one quarter of the Hi speed horsepower. The other types can be found here. Also know as Dahlander or Consequent-Pole type.
NEMA starter application data
MTW