infinity said:The 'hot' you got working on is dead but that neutral is still carrying a load back home
This is completely dependent on where in the circuit you're working. If you're changing a ballast with the hot leg de-energized to the fixture the neutral at the fixture will not be carrying anything regardless of the number of circuits connected upstream of that fixture.
It is not dependent on where in the circuit you're working.
The neutral present with the hot leg de-energized to the fixture is the exact same neutral that is present at every other point in the circuit. The different sections and branches of the neutral will carry different loads and will register different current flow but the entire neutral multi branch is electrically identical. If you lose the neutral HR, every single point that the neutral is present, at every single box regardless of which phase conductors are also present at any individual box, every single point will be "hot", as long as any one of the multi phase breakers are still on.
David