A/A Fuel GTX
- WI & AZ
- Electrician
I've used mud rings both metallic and plastic for LV devices for years without any problems.
Sure it does. You can't do something non-NEC-compliant and say "But, it's in the specs that way!"Cause if he asks for those specs and its different than the NEC, NEC does not override the specs.
Really?
Can you show us instructions included with the listing or labeling of a 'mudring' that requires that they be used with a box?
BTW, Chapter 1 (110.3) does not apply to Chapter 8 unless it is mentioned in Chapter 8.![]()
Are you sure these were not fire rated walls?
Mudrings have been used for telco apps for years and before I could crawl and that was more than 40 years ago. Tell that inspector to show you the code or show you the money. If its in a fire wall don't bother cause you be on the wrong here.
Now I 've heard is all failing an inspection for a mud ring without a box because it's not listed that way.
Hey I used to cut the back off a NM box now you can buy them that way.I'd like to hear what he said about this.
By the way those products from Erico are a bit easier to use and they have less bulge in the wall by the way.
I know, and they are cheaper too! by about 1/3. But that is an inferior product because the sheet rockers bury them and they get the snot knocked out of them. I'd like to see the sheet rockers try to bury my 5/8"'s mud ring! Also, I even used the super flat screws to mount them so they did not bulge.
I know I am beating a dead horse because of article 100.3B, however, I spoke to RACO, and they are willing to write a letter stating that I did not ruin the UL listing by using it ni this application. Ultimately, I think he will make me change it. But how many of you go back later because those LV mounting brackets are loose or flimsy...? NEVER had a problem with a mud ring EVER. Simply put its not right and the code is written for "minimum standards" if I exceed them why should I be punished.
I recently installed as I have many times before mud rings mounted to studs(metal) for data and phone terminations. Well an inspector came in and failed this installation the reason given was that the product was not UL listed for this application. Through various conversations with inspectors, manufacturers, UL reps, it seems the mud ring UL literature does not mention this application specifically but in using both products a mud ring is much sturdier and on a big job as this is less prone to damage and will support my device plate better. So my question is where in the code does it require or state what kind of box needs to be used for this application and does the code require it to be UL listed for that application I would really like to fight this more on principal than anything.
This "inspector" is a moron and it's people like him that are such a problem in the trade
That would be the ONLY reason I could think of - and still be a UL listing violation.... For the sheet rock assembly...Are you sure these were not fire rated walls?
Wouldn't go that far.... But I HAVE....This "inspector" is a moron and it's people like him that are such a problem in the trade.
Plaster rings can be mounted separately eliminating the need for an electrical box for low-voltage applications
Otherwise it is no different....Offset design of MEB1 and use of CADDY Part # SMS8 low profile self-tapping screws (not included) eliminates drywall bulge
Maybe not in homes or some small retail businesses, but as for schools hospitals, doctor offices, data centers, warehouses/office buildings. These are the types of jobs that I do. I have seen it on all spec codes. Yes spec codes are diff than most NEC codes, but if its in the specs, then DO NOT whip that code book in front of the inspector. Cause if he asks for those specs and its different than the NEC, NEC does not override the specs.
Can an inspector enforce specs? Or is he just there for NEC requirements?
Hmmm... Lesson - 'don't bend...' :roll:Thank you all for all your comments, and lets hope we all learned something...still not sure what exactly, but there's gotta be a lesson in there somewhere.
If the specs or plans are stamped by an engineer, I think the inspector can either enforce them, or require a set of revised, stamped specs.