Painters, Recepticle Faceplates
Mike Furlan
Lemont Il
Painters will remove the faceplates from recepticle faceplates before painting.
Taking off the faceplates exposes live conductors.
Should they be required to de-energize, and lock out and tag out the circuits involved based upon NFPA 70E?
Which part of 70E are you referring to? 130.2(A)? Then give them some gloves 130.7(A).:grin:
I'm not making light of this, I think it's and interesting question.
IMO if they remove the plates then it's their problem when it comes to compliance.
What is better, to remove them or paint over them? Myself I lkke them removed so they don't get covered wuit several coats of paint.
Lou
I'm with Bryan! You trimmed out too early. There should be VERY LITTLE touch up after trim out. Painters and electricians are usually the last ones out, but almost simultaneously.
The prohibited approach boundary for 120 volts is "do not touch" so voltage protection is not required to remove the covers. I doubt that there is enough current available at that point in the circuit to required any arc flash protection. I expect that the only thing 70E would require would be a long sleeve non-melting fabric shirt.
Rob, do you have the 70E? I believe it is the employers responsibility to establish a safe working environment.
110.3
If the EC installed the plates and energized the receptacles hasn't he already done all that's required? If the painter wants to remove the plate why should the EC be involved at all? If the painter removes the cover on a panel and blows himslef up is the EC responsible for that too?
How about 1301.1
"Justification for Work. Live parts to which an employee might be exposed shall be put into an electrically safe work condition before an employee works on or near them. . ."
But you can only work with live parts if to de-energize would cause additonal hazards, or is infeasible.
Neither condition is met.
There is no reason that all live parts could put in a safe condition.
No the EC would not be responsible, but the painter's boss, and the ES&H guy who signed off on the work would be.
Painters problem all the way. If I was there before the painter was done then I can tell you that painter IS LATE. That painter better be leveling those plates and all the screws facing the same way.
OH I hate when they touch my work before it's accepted.,.....:mad:
Your not working with live parts unless you cross the prohibited approach and are not working near live parts unless you cross the restricted approach boundary. For a 120 volt receptacle both of these boundaries are listed as "avoid contact" (do not touch) in Table 130.2(C). The removal of the device covers is not working on or near live parts, the only issue would be arc flash protection, however the protection category would most likely be "0" requiring only long pants and long sleeve shirt of non-melting fabric.
What if it is a repaint you are making assumptions that all work is new work.
Sorry ZBANG you beat me too it.