Sierrasparky
- USA
- Electrician ,contractor
Well just think of it as saving space, we have two topics in one thread![]()
I get ya :grin:
240.4 itself is where this code starts, and says to 'use 310.15, unless permited, or required by A though G....'OK, let's print it out:
Hightlighted in blue: If my installation falls under (E), ~ or (G), then I use the appropriate section that applies. Otherwise, I'm stuck with the small conductor rule of (D)(1)-(7).
240.4(D) starts out with references to (E), ~ (G). It says that if your installation is a tap, a transformer secondary, or anything specifically listed in (G), YOU USE THAT SECTION. If your installation DOES NOT fall under (E), ~ or (G), then it says to use (D)(1) through (7).
Yeah.... there is enough confusion...Why do you keep including (F) when it only says (E) OR (G) ?
The same coud be said for the individuals who feel 28A on #12 for a compressor motor is just fine... While I obviously don't agree with that - the same individuals feel 20A OCP on #14 taps to 600W of lighting is not kosher.... A contradiction to say the very least.~~~
But.......for all the freak out, "oh my God, you hacks are going to burn the place to the ground" crowd in this thread, I have to ask, how is a #14 switch leg with 20A OC any more dangerous than a #14 fixture whip or fixture wire on 20A OC?
...all this talk of whips and switches......some of you guys need anger management![]()
And this is my understanding of 240.4(D) - these smaller conductors would be damaged in fault conditions - and that was the reason for limiting the OCP on those.... In recent debate on the topic I found the Bussman litature that they used to justify the use of 'their products' to allow 16 AWG - stating that 'thier products' could clear the fault current before conductor damage. And it is my understanding that the formulas used to create T310.16 ~ T310.18 were developed for underground ducts - and were not suited for "smaller conductors".... Hence the limitations of OCP on them... That's just my take on it....Also keep in mind that a #14 can withstand 97.31 amps for 5 seconds before it starts to damage the insulation, much longer than it will take to clear a breaker on a fault.
I agree even if you plan to use the correct OCP for the conductors down the line - it is still a bad practice IMO....yes but what does that have to do with an unknown load ? Problem here is you allow the #14 because you see 5 light fixtures NOW. 5 months from now they add 20 more and the electrician looks at breaker size and ballast amps. He will never know about the cheap a-- that used #14 to save $1. He will more times than not even check amps now. I have many times added 1 or 2 more at 277 without asking or checking in factories because it would easily take an extra hour and 1 more man and shut down operations. I must rely on past electrician to not do something as stupid as under size a switch leg. that looks looks like a #12 circuit. I would checks amps at breaker and if close to 16 will walk away. Only hacks do garbage work like changing to #14. If your one of them please don't let me ever know. When we walk in on remodels we MUST assume what is there is correct and safe and only deal with what we add. If your one of them please then please find some job your qualified for , perhaps a garbage truck. Your messing with lves.
Correction - three topics - all on the same code section....Well just think of it as saving space, we have two topics in one thread![]()
THHN is not a wiring method either. The conductors would be allowed in a raceway. 402.7.Fixture wire is not a wiring method. Where between the outlet and fixture do you propose concealing the wire beneath the building finish?
30 volt max if a power-limited circuit (725.41(A)), if a higher voltage than classified as "Remote-Control and Signalling Circuits" (725.41(B)).What if I considered the switch leg a Class I nonpower limited circuit? It is used for the remote control of the luminaire. There are lighting systems on the market that use the Class III designation between the luminaire fittings.
And not just between the outlet and the fixture, but from the switch to the outlet to then connect to the luminaire.
It is allowed. 240.4(E)(3) > 240.5(B)(2) > 240.5(B)(2)(2) // Article 402.
Concealed. Rendered inaccessible by the structure or finish of the building. Wires in concealed raceways are considered concealed, even though they may become accessible by withdrawing them.
400.8 Uses Not Permitted. Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following:
(5) Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings
Not quite:...And not just between the outlet and the fixture, but from the switch to the outlet to then connect to the luminaire
(1) As a substitute for the fixed wiring of a structure
Well then, let me start over since I'm off on a tangent somewhere. Not paying attention I guess.I'm not talking about flexible cords or cables(400), I'm talking about fixture wires (402).
Different. Not the same.
OK. Starting over.And not just between the outlet and the fixture, but from the switch to the outlet to then connect to the luminaire.
402.11 Uses Not Permitted. Fixture wires shall not be used as branch-circuit conductors except as permitted elsewhere in the Code.
Branch Circuit. The circuit conductors between the final overcurrent device protecting the circuit and the outlet(s).
Lighting Outlet. An outlet intended for the direct connection of a lampholder, a luminaire (lighting fixture), or a pendant cord terminating in a lampholder.
OK. Starting over.
How is what you propose not in conflict with this:
What a mishmash of topics.
Let me add the definition of an lighting outlet box:
Branch circuit conductors stop here and fixture wires start here.
Remind me, what is the full list of topics again?
1. 14 AWG on a 20 amp OCPD.
2. :-?
No conflict, just some page flipping. While 402.10(2) simply says "for connecting luminaires to the branch-circuit conductors" with no respect to location, "elsewhere in the Code" (240.5(B)(2)(2) for instance) allows up to 100 feet of 16 AWG to be tapped to the branch circuit.
So the NEC either allows these conductors, say, in a raceway (402.7) to extend from a "point on the wiring system at which current is taken to supply lighting equipment" (Art. 100 / Outlet) to a luminaire(s) some distance away, or they are talking about really big fixtures.:grin:
You haven't been reading along!
mostly comments, like this one, unrelated to the OP, in which the Post-er [me] is spouting off on a subject of humor or some other ancillary issue in order to increase his total post count!!:grin:But what are they?
Suppose you have a metal faceplate on a receptacle, should the ground be up or down?:grin: