masterselectric
Is #2 SER good for 100 Amps?
Ser or seu, residence or not, if this is a sub panel does it carry the full load of the service or not.Is #2 SER good for 100 Amps?
I'm betting aluminum since #2 aluminum is good for a dwelling service. I am also betting that it's a dwelling but I can guess no more. :grin:Is it copper SER or alumimum?
Since we're speculating I'll add my 2 cents.
I bet it's a resi sub panel and he got bagged for unsing #2 AL protected at 100 amps.
What code cycle is in use? 2005 or 2008. Big difference concerning feeders
The 2005 code cycle excluded 334.80 for interior installations.(under Article 338.10. B-4a) Now in the 2008 code that sentence was removed. Now you have to take temperatures limitations on conductors. SER 2-2-2-4 on 100 amp breaker feeding a MLO panel acceptable in the 2005 code not so in the 2008.
In this area of the world, the inspectors are of the opinon that 338.10/334.80 are to be taken into account and ampacity adjustments
do preculde #2 AL SE to be used as an interior wiring method on a 100 amp service.
I know of nothing to support that opinion.![]()
Dennis knows I have to add my 2? worth. :grin: