Is #2 SER good for 100 Amps?
Is #2 SER good for 100 Amps?
Ser or seu, residence or not, if this is a sub panel does it carry the full load of the service or not.Is #2 SER good for 100 Amps?
I'm betting aluminum since #2 aluminum is good for a dwelling service. I am also betting that it's a dwelling but I can guess no more. :grin:Is it copper SER or alumimum?
Since we're speculating I'll add my 2 cents.
I bet it's a resi sub panel and he got bagged for unsing #2 AL protected at 100 amps.
What code cycle is in use? 2005 or 2008. Big difference concerning feeders
What code cycle is in use? 2005 or 2008. Big difference concerning feeders
The 2005 code cycle excluded 334.80 for interior installations.(under Article 338.10. B-4a) Now in the 2008 code that sentence was removed. Now you have to take temperatures limitations on conductors. SER 2-2-2-4 on 100 amp breaker feeding a MLO panel acceptable in the 2005 code not so in the 2008.
In this area of the world, the inspectors are of the opinon that 338.10/334.80 are to be taken into account and ampacity adjustments
do preculde #2 AL SE to be used as an interior wiring method on a 100 amp service.
I know of nothing to support that opinion.![]()
Dennis knows I have to add my 2? worth. :grin: