LarryFine
- Henrico County, VA
- Electrical Contractor
Noooooooooooooooooooo!I might just close and then delete this thread, just to keep the old record intact.
Agreed. Now we need to define that line by deciding which receptacle is "the end of the premise wiring."
Almost everything is premises wiring...see Article 100.Agreed. Now we need to define that line by deciding which receptacle is "the end of the premise wiring."
I agree 100% with Charlie on this one.It does not use energy. It merely passes it further on down the line. Your device no more fits the definition of utilization equipment than does an extension cord. But don?t be concerned. This point is not going to make or break anyone?s argument on the subject of whether your device is NEC compliant.
Same here. I still consider the entire package a glorified extension cord that uses approved-for-in-wall-use components for the in-the-wall portion.I agree 100% with Charlie on this one.
If it was premises wiring using extension-cord components, it would not be NEC compliant. That alone proves it can't be premises wiring.
Mainly that they're not designed for use with solid conductors in general, and, I believe, NM in particular.Any NEC "not permitted" sections with reference the use of NM or TC cable with 5-15R and 5-15P end connectors?
Doing the same, I'm thinking of constructing a portable mock-up of an inlet and a receptacle in a pair of OWB boxes on a piece of drywall, and demonstrating the installation to my two favorite chief inspectors.Just thinking aloud.
Anyone have a miniature panel TV to lend me?
"in use" is when the cord is plugged in and energized. It is at that point fufilling its function: to extend the point of connection to a power source.So the next BIG question:
If your not certain claim is to bias the purposeful use of the cord specifically to the "words" "temporary use" is a permitted use of a cord-set, then when, at what time is the cord actually in use? When the appliance is on? plugged in? What if the connection to the appliance involves a "vampire" circuit cutoff device?
UPS devices, remote power taps, etc are not the same as cord sets.Is there a rule which states if a surge protector/UPS connected to a premise wired outlet can only be plugged in temporary?
These devices have specific purpose do they not? They have flexible cord-sets. Where is the permitted use for these, the rules to apply, the duration of time to use. Is there a rule the SP/UPS is not permitted to supply power to a cord-set?
I'm not clear if one exists, is there?
The NEC makes a distinction between the flexible cord attached to the appliance and other flexible cord uses.ie, if the cord is connected to the premise wiring outlet and is connected to an appliance as allowable in 400.7, the remise of 400.8(1) says it's not allowed, expect that 400.8 heading states unless specifically permitted in 400.7, so which is it?
Are there two sides of the NEC fence in these conditions? Which are we to apply as it obviously is not well defined as we find in this HUGE thread.
Flexible cord is not a permitted method for general wiring. There are specific applications where flexible cord is permitted to extend branch circuits. One case is with luminaires. There is also an exception that allows electric discharge lighting with inlets to be supplied by cord pendants with cord connectors. Just because there is an exception for this particular case does not mean we can use inlets and connectors as wiring methods everywhere because it is not a permitted wiring method for general wiring.The term "temporary", does not appear anywhere in 400.7 or 400.8, nor as a Definition in Article 100, nor in UL as to cord-sets.
Are we to apply the ambiguous term as to ONLY WHEN it is actually energizing an appliance?
Is it a violation if the cord-set is only plugged into the outlet and nothing else?
It's not substituting, it's NOT in use, is there violation if we follow 400.7 or 400.8?
Perhaps you can elaborate on the vampire device. The primary use for the PowerBridge is to plug an extension cord into an existing receptacle in order to power an added receptacle permanently installed at a different location.In the case of the PowerBridge, it has "specific purpose" to energize the in-wall EXTENSION, using compliant materials as called out in code, to an utilization device, (appliance) (TV). ONLY, not to replace something which is not already in place within the structure. If something is already "part-of", the outlet used to energize the cord-set, then how is it subtitution using a cord going to define itself? It's not replacing it's purpose if it exists to supply energy to an appliance.
If the TV is being energized through say a "vampire device power supply" cutting power to the appliance when not in use, at what point is the appliance being enerigized? Always? temporary?
The point was that an inlet as a separate device is intended to be used on utilization equipment. Could using the inlet as a feed to a section of NM cable (what PowerBridge does) be seen as using the inlet for something other than what was intended? Just a question.The PowerBridge is also not a Motor.
Other than using the word inlet, this reference has absolutely no application to the PowerBridge.
Justin are these units designed for one flanged outlet to feed one receptacle. What stops someone from looping 5 tv's to one flanged inlet? I guess I am asking is your product approved or listed for more than one or just one receptacle?
Just seems odd to summarily dismiss paragraph (B) by saying the specifics are ONLY covered elsewhere when it is obvious that paragraph (C) also has some important instructions for us.So we can pretty much ignore 210.50(C)?
You can. I'm not.
That would require someone with a need to flail in the first place. We are discussing the possibilities of the device conflicting with code. I have no dog in the hunt. The end result won't make or break my day. It is not about some act of desperation but about being thorough.Can you say, "Flailing about, grasping at straws?"
I have no idea what the sentence means.Don, respectfully, as I described in post 602, with Article 100 to guide basis of description, is the cord-set still a substitution of the PowerBridge, if it is possibly allowable/permitted in regards to 400.7 as I cite bias to permitted use.
Because a listing cannot change a code rule and that is what is happening with this listing.Our Listing applies specific intent and purpose of use the INLET to a single-pole outlet conductors, no to energize a structure premise wiring.
Why is our listing being thrown out for all reason of implied specific purpose?
I understand an AHJ can decide not to apply Listing, its subjective.
Are we to always assume the AHJ will not accept Listing as a basis to apply safety as a tested product?
We could just accept that the device is listed and move along. The problem is that we already have at least one jurisdiction opposed to the use of the device. I think our effort here is to discuss every possible angle, not from the aspect of "grasping at straws", but to see if we can leave no stone unturned.
A defense is really worthless if there was no effort on the part of the prosecution. I have no problem with either role, but let's at least make a concerted effort to explore every avenue.
As I have said before, this device is no more a danger than many things we use that are deemed acceptable now. How is this device any different than feeding discharge lighting inlet through a flexible cord? Flexible cord has been allowed to extend branch circuits under certain conditions. Why not this condition? Would the NEC make an exception in this case? The fact is that this specific use of flexible bale for extending branch circuits has not been allowed yet, IMO.
Without some clarification, this device can continually be called into question. Hopefully we can explore the possible code conflicts so a proposal can be put forth with a ruling that is clear enough to settle any questions that might arise in the future.