What about a fastened-in-place lighting fixture, such as under-cabinet lighting, that comes with a permanently-attached length of lamp cord? We can't plug them into counter-top receptacles.I can see no code compliant use of a cord that supplies power to the fixed wiring of the building other than an Article 702 application or a Article 590 application.
Blade configuration is not the issue.If the INLET device instead was a 3-prong IEC type C14 male panel mounted to a wall-plate.
...
Would these devices provide a possible different application for using a power supply cord to extend circuit power from an existing receptacle outlet?
It is not the blade configuration. It is the fact that the appliance cord's attachment plug is required to be energized by a receptacle. FWIW, the female connection on the end of an extension cord is not a receptacle but a cord connector and the male end is the attachment plug. Installing extension cords to get around that receptacle is substituting for the fixed wiring.Basis is applied as these connectors have SPECIFIC use as to power connectors for utilization equipment. These could be viewed to not be considered a substitution as they would carry specific use and be a differential of standard 5-15R type receptacles.
Not just me. It is common knowledge that extension cords are temporary. The places where flexible cords are allowed otherwise are specifically spelled out in the code.Yes, extension cords are not fixed premise wiring, that is implied as an extension cord can be removed, is portable, replaceable and is not attached to the structure unless permitted in some sections of Code.
You continue to cite the word "temporary" without actual basis. It's your inserted word.
Q. Is there a section in the Code that restricts the use of extension cords?
A. No. The NEC is an installation standard, not a product standard. However, listed extension cords should be used in accordance with the listed instructions, but this isn't a Code requirement. According to UL's Web site, extension cords aren't intended to be used as a substitute for the fixed wiring of a structure. So basically, an extension cord is only for temporary usage.
The night's still young.I just want to say thanks to everyone participating in this thread for keeping it so civil, this post is # 560 and there is not a single deleted post, thanks to all.
In case it's not obvious, I agree.BTW, I still say it's legal.
The only reason I suggested it was that there was a question as to whether it provided the receptacle for the appliance. In order for it to do that, it needs an acceptable wiring method on the front end and, as you noted, the extension cord won't get it done.The question was addressed to Bob, but I?ll give my answer anyway. I never saw any portion of this product as constituting a portion of the premises wiring system.
If it is going to be an alternative, it must use approved wiring methods.OK, we agree the PowerBridge is not part of the premises wiring system. Then I can't see how it is substituting for a hard-wired receptacle directly behind the TV. It is instead an alternative, and you end up with a different thing.
No. The appliance cord is not in question. It only requires a receptacle for the attachment plug.Under the definition of substitute you seem to be using, any utilization equipment that can be either hardwired or cord-and-plug-connected must be hard-wired. Otherwise the cord is substituting for fixed wiring.
A violation unless it was specifically allowed.What would you call an affixed extension cord?
So call it an extension cord. Where is permanent use of an extension cord to an appliance allowed?I'm not clear which of the two receptacles in a Powerbridge installation you are referring to here. I would say that the premises wiring system ends at the first receptacle (into which the Powerbridge cord plug is inserted), and you are running some additional wiring in the wall as a way to avoid running a long power cord directly to that first receptacle. So you are not substituting cord for in-wall wiring, you are substituting in-wall wiring for part of the cord.
Not so fast. The utilization equipment can have its own cord and that cord may have an attachment plug. That is specifically allowed.Let me try to rephrase my argument about powerbridge and its relationship to utilization equipment that may be either cord-and-plug-connected or hardwired.
(1) If 400.8(1) means "don't use a cord in any place where you could use a Chapter 3 method", then any utilization equipment that could be hard-wired would have to be hard-wired, you couldn't use a cord with it. (2) That seems absurd, so we reject that interpretation.
Well, there's a post that should be deleted if I ever saw one. :grin:I just want to say thanks to everyone participating in this thread for keeping it so civil, this post is # 560 and there is not a single deleted post, thanks to all.
BTW, I still say it's legal.
Roger
I can think of a couple, but they are pretty out there:I can see no code compliant use of a cord that supplies power to the fixed wiring of the building other than an Article 702 application or a Article 590 application.
With approved wiring methods. Got a particular fixture in mind?What about a fastened-in-place lighting fixture, such as under-cabinet lighting, that comes with a permanently-attached length of lamp cord? We can't plug them into counter-top receptacles.
How are they to be powered? How do we interface them with building wiring?
I took Don's statement to only include situations where power travels through building wiring after going through a cord.What about a fastened-in-place lighting fixture, such as under-cabinet lighting, that comes with a permanently-attached length of lamp cord?
How is a cord that is directly attached to the light fixture supplying power to the building wiring system?What about a fastened-in-place lighting fixture, such as under-cabinet lighting, that comes with a permanently-attached length of lamp cord? We can't plug them into counter-top receptacles.
How are they to be powered? How do we interface them with building wiring?
Using a cord (cord connector) to power the equipment cord is where the trouble starts. The code says the attachment plug shall be energized from a receptacle outlet.
That's the way I see that it reads, except for portable equipment and temporary use.OK, so 400.7(B) is your reponse. So does "energized from a receptacle outlet" mean "the attachment plug must be inserted into that receptacle outlet"? If it does, then 400.7(B) bans all extension cords.
Yep. We all luvs the extension cords. Doesn't mean that the NEC does.That seems unlikely, so I can't accept that interpretation.
That doesn't sound logical. That means the receptacle must be somewhere in the solar system, or thereabouts. It makes more sense to say that if you have an attachment plug, then you need a matching receptacle to plug it into.So instead, "energized from a receptacle outlet" means "power from the service passes through a receptacle outlet before reaching the attachment plug." In the typical Powerbridge installation, this requirement is met: the first receptacle (that the Powerbridge cord is plugged into) is a receptacle outlet, and the appliance attachment plug is energized from that receptacle outlet.
Cheers, Wayne
Under your interpretation, where does 400.7(B) provide relief for portable equipment and temporary use?That's the way I see that it reads, except for portable equipment and temporary use.
Of course you need a matching receptacle, the Powerbridge install provides that. The question is whether you need a receptacle outlet, or if you can plug cords into other things. Can I plug a cord into a cord-and-plug connected UPS? That's not a receptacle outlet, the UPS is not part of the premises wiring system.It makes more sense to say that if you have an attachment plug, then you need a matching receptacle to plug it into.
I have more than one extension cord in use in my house that hasn't been unplugged in over 12 years. One is attached to the house by cable clips that hold it off the floor along the baseboard.So call it an extension cord. Where is permanent use of an extension cord to an appliance allowed?
I pictured 120v pucks, but there are other cases of rubber cords that directly wire-nut with building wire, such as commercial exterior building lighting.With approved wiring methods. Got a particular fixture in mind?
I took Don's statement to only include situations where power travels through building wiring after going through a cord.
How is a cord that is directly attached to the light fixture supplying power to the building wiring system?
All right. Let's take one of those pre-packaged under-cabinet lighting sets that comes with a switched multi-receptacle controller and several lights, each with a plug. A simple plug'n'play setup. (Where the light controller plugs in is a separate discussion.)I took Don's statement to only include situations
where power travels through building wiring after going through a cord.
Under your interpretation, where does 400.7(B) provide relief for portable equipment and temporary use?
Where it sits is of no importance. We would have to define portable as the NEC does not.In regards to portable equipment, are you saying that if my TV sits on a shelf on the wall, instead of be fixed to the wall, Powerbridge is OK?
That's where the fun begins. To me, the NEC oversteps its authority when it starts telling us what to do beyond the installed wiring. But they do it anyway.Of course you need a matching receptacle, the Powerbridge install provides that. The question is whether you need a receptacle outlet, or if you can plug cords into other things. Can I plug a cord into a cord-and-plug connected UPS? That's not a receptacle outlet, the UPS is not part of the premises wiring system.