Lets say I've done a load calculation and determine that the load is under 380A and thus I can use a 500MCM cable. Can I use this 500MCM cable on a 400A breaker since I can use the "next size up rule"?
The way I understand it though I would not be able to use the 500MCM cable on a 450A breaker since this 450A brekaer is not the next size up. Is this correct?
So if I had a 450A breaker I would need to use a 600MCM cable at minimum. Is this correct?
When a breaker is upsized for transformer inrush then must you still also increase the cable size so that the cable size is protected by the "next size up" rule as well?