I have installed a pole mounted 200 amp load center/meter enclosure. Plan was to split that into 2 100 amp feeders , 1 for house and one for garage. Load calc. was way under 100 amps for the house size . Have already run #2 aluminum into the basement . Modular home was delivered with a 200 amp panel. My question is Can I still feed it with the #2 wire as long as I am protecting it with the 100 amp Brkr? Thanks for any help.