david
 - Pennsylvania
I don?t know if your clincher is a strike or a curve ball
? Now you can go to 250.32(A) for the electrode requirements.
You could if they where required;
As you posted and high lighted in red
(2) Feeder conductors shall be installed in compliance with
250.32(B).
Note it does not say the feeder conductors shall be installed in compliance with 250.32 it does say 250.32(B) That seems deliberate in leaving 250,32(A) out of the requirement your trying to imply because grounding electrodes are mentioned in 250.32(B) they have to be installed.
I would agree if the rule said shall be incompliance with 250.32 it does not it says 250.32(B)
250.32(B).