 - Illinois
 - retired electrician
Yes, I am very aware that a grounding electrode has to be in contact with the earth. That fact really has nothing to do with my comments.The debate that Bob and Don are having with me is the term ?present at? and how this would mean outside the building.
What I have repeatedly pointed out is that in order to be a grounding electrode it must be in direct contact with earth.
This is not only the definition but the requirement of all the grounding electrodes except the building steed and a concrete encased electrode to wit the building steel if not in contact with earth must be connected to one of the electrodes that are in contact with earth and the concrete encased electrode which must be in the footer and the footer in contact with earth.
I now present the question of just how this can be accomplished and not be outside the building. How can an electrode be in contact with earth and be anywhere but outside the building. I patiently await an explanation on how the electrode can be anywhere but outside the building.
It remains my opinion that a metal underground water pipe that has at least 10' of pipe in contact with the earth outside of the building is not present at the building unless it enters the building. We will continue to disagree on this issue until I see a published comment in the ROP or ROC or FI from CMP5 that says otherwise.