Again you are talking about the utility side of the water system
And this has to do with this conversation how?
Again you are talking about the utility side of the water system
In my area the utility side of the water system normally enters the building as the water meter is inside, but what does that have to do with anything. There are a couple of water utilities that used a dielectric fitting just outside of the building to isolate thier piping from the electrical system. That is rare around here now as most have switched to non-metallic mains.Again you are talking about the utility side of the water system
The purpose of the words "present at the building" is to require the use of electrodes that are not "made" electrodes no matter how they got there.and those water pipes are never present at the building they are installed by the plumbing contractor
Mike,An old building is being renovated to a small convenience store. Due to the parking lot the service is being moved to the opposite end of the building.
This old building had air terminals that were connected to a #2 ground ring that circled the building and was connected to the outside service panel which the owner has demolished as it is to be moved. He cut the conductor from the service to the ground ring some feet from the building.
A new metal roof has been installed and the air terminals removed along with all the grounding conductors to the ring which were cut several feet from the building and removed. The inspection department has records of the inspection of the air terminals and the ring.
In this small jurisdiction there is one code official that does all five trades, building, mechanical, plumbing, electrical, and fire. He has been here forever and was the one who inspected the air terminal installation some years ago.
When the new service is installed will it be required to connect to this existing ground ring? Based on this thread this existing ring is NOT present at the building but somewhere out there in the yard therefore not required to be used.
If you were the electrical inspector what would you say?
Don I have answered this more than once so please read slowly and carefully.
From the point of supply by the utility or from the well that is supplying water to the building is present at the building.
Show me language that says anything different.
250.52 Grounding Electrodes.
(A) Electrodes Permitted for Grounding.
(1) Metal Underground Water Pipe. A metal underground water pipe in direct contact with the earth for 3.0 m (10 ft) or more (including any metal well casing bonded to the pipe) and electrically continuous (or made electrically continuous by bonding around insulating joints or insulating pipe) to the points of connection of the grounding electrode conductor and the bonding conductors. Interior metal water piping located more than 1.52 m (5 ft) from the point of entrance to the building shall not be used as a part of the grounding electrode system or as a conductor to interconnect electrodes that are part of the grounding electrode system.
Where does it say that the pipe must enter the building in order to be present at the building?
250.50 Grounding Electrode System.
All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system. Where none of these grounding electrodes exist, one or more of the grounding electrodes specified in 250.52(A)(4) through (A)(8) shall be installed and used.
It clearly states that any of the first 7 that are present at each building and at least six of these does not enter the building at all. By your definition they are not present.
Now what about the ground ring above
So let's say for argument sake you're correct. Where in the NEC will someone find the maximum distance from the structure that the metal water pipe has to be for it to qualify as an electrode even though it doesn't enter the building?
There in nothing in this post that answers my question.Don I have answered this more than once so please read slowly and carefully.
From the point of supply by the utility or from the well that is supplying water to the building is present at the building.
Show me language that says anything different.
250.52 Grounding Electrodes.
(A) Electrodes Permitted for Grounding.
(1) Metal Underground Water Pipe. A metal underground water pipe in direct contact with the earth for 3.0 m (10 ft) or more (including any metal well casing bonded to the pipe) and electrically continuous (or made electrically continuous by bonding around insulating joints or insulating pipe) to the points of connection of the grounding electrode conductor and the bonding conductors. Interior metal water piping located more than 1.52 m (5 ft) from the point of entrance to the building shall not be used as a part of the grounding electrode system or as a conductor to interconnect electrodes that are part of the grounding electrode system.
Where does it say that the pipe must enter the building in order to be present at the building?
250.50 Grounding Electrode System.
All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system. Where none of these grounding electrodes exist, one or more of the grounding electrodes specified in 250.52(A)(4) through (A)(8) shall be installed and used.
It clearly states that any of the first 7 that are present at each building and at least six of these does not enter the building at all. By your definition they are not present.
Now what about the ground ring above
Since there is no maximum distance for any made electrode, this statement would mean that any metal underground water pipe any where in the world would have to be used as a grounding electrode.at the same distance that would be the maximum allowed for a ground rod or any other electrode.
There in nothing in this post that answers my question.
You have not read my posts in the way I have written them. I have stated that the term "present at the building" does not apply to made electrodes.
As far as your far fetched example of the unknown ground ring, if the contractor does not know it exists how can he be expected to find it and connect to it?
Since there is no maximum distance for any made electrode, this statement would mean that any metal underground water pipe any where in the world would have to be used as a grounding electrode.
As the current contractor who has never been in the building before, I have no knowledge of that ground ring so there is no way I can think about it.Then why are they mentioned in 250.50? I do believe it clearly says "All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shal............"
The inspector is well aware that the ground ring is there as was outlined in the post.
So what do you think about that existing ring?
As the current contractor who has never been in the building before, I have no knowledge of that ground ring so there is no way I can think about it.
In this small jurisdiction there is one code official that does all five trades, building, mechanical, plumbing, electrical, and fire. He has been here forever and was the one who inspected the air terminal installation some years ago.
When the new service is installed will it be required to connect to this existing ground ring? Based on this thread this existing ring is NOT present at the building but somewhere out there in the yard therefore not required to be used.
If you were the electrical inspector what would you say?
I have addressed it. There are always special unusal cases and this would be one of them. As the contractor I am not aware of this ground ring so there is no way I could think about it or connect to it. If made aware of it, I would make the connection if I am paid to make it.read it again,
The inspector is well aware of the ring so the question is not about the knowledge of the contractor but what will the inspector require.
For the sake of this discussion either put yourself in his shoes and make the call or think of it that he told you that it was present.
Don't avoid the question but address it.
There is nothing found anywhere in the NEC that would lead me to believe that the term ?present at? means that it must be inside the building but there is verbiage found in 250.52(A)(1) that clearly states that the only part of a metal water pipe that is electrode is that part that is in direct contact with earth which means that it cannot be inside the building and be the electrode.
There is nothing found anywhere in the NEC that would lead me to believe that the term ?present at? means outside the building.
So there we have it, we will remain in disagreement.