As discussed via telephone, 250.50 requires all grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served is required to be bonded together to form the grounding electrode system. The NEC does not define “present at the building”, such questions should be directed to the authority having jurisdiction. Section 250. 52 (A)(1) requires metal underground water pipes in direct contact with the earth for 10 feet or more (including any metal well casing bonded to the pipe) to be electrically continuous or made electrically continuous by bonding to be used as a grounding electrode.
Jean M. Blanc
Associate Electrical Engineer
National Fire Protection Association
Important Notice: This correspondence is not a Formal Interpretation issued pursuant to NFPA Regulations. Any opinion expressed is their personal opinion of the author, and does not necessarily represent the official position of the NFPA or its Technical Committees. In addition, this correspondence is neither intended, nor should be relied upon, to provide professional consultation or services.