Michael15956
- NE Ohio
Hey, I'm willing to lose this debate, buy you guys got to come up with a better agreement.
Looks to me like the score is 4 to 0, two outs bottom of the ninth and all your bats are broken!
All we need now is for "the fat lady to sing" and debate lost!:lol:
A fitting secured to conduit is part of the conduit and this section does not eliminate fittings. Come on guys, the section requires a threaded connection, that is it!
LOL,yeah, but looks to me like the fat lady has lose her voice! AND, the majority is not always right.
OK, just for fun here, my debate is not about the strength of the said install. It is about the meaning of Section 314.23(F). Given your described install has more strength, but that is not what we are debating. 314.23(F) list five requirements: an enclosure that is support by a raceway shall: 1. not exceed ba,ba, ba. 2. shall has threaded entries or hubs. 3.two or more conduits 4.threaded wrenchtight. and 5. ba, ba, ba.
So, the enclosure cannot be over a certain size and the enclosure must have threaded entries or a hub, that is identified. Now it has been written here that a PVC fitting is not a conduit, not buying that. Hmm, what is a hub? Maybe a hub might be a fitting.
Once again, I believe that this section really wants a treaded connection as one of the said requirements.
Well I don't know what the code making panel that made majority of the requirements for this application was thinking about, but the strength and reliability of knowing the thing will not easily be broken or pull apart would be something I would be concerned about if I were a part of the panel. I have seen many compression fittings have raceways pull out of them including supposably cemented PVC fittings, I have also seen probably even more PVC terminal adapters that snap off right at the point of transition from thread to the body that the raceway slips into. Neither is a good choice for this use even if they would be allowed, IMO they are not allowed.
(B) Support of Luminaires. For the support of luminaires
or other equipment not described in 352.10(H).
H) Support of Conduit Bodies. PVC conduit shall be
permitted to support nonmetallic conduit bodies not larger
than the largest trade size of an entering raceway. These
conduit bodies shall not support luminaires or other equipment
and shall not contain devices other than splicing devices
as permitted by 110.14(B) and 314.16(C)(2).
You're still forgetting/overlooking/don't want to see, the part about PVC not being permitted to support the box. As far as 352.12(B), the phrase "or other equipment not described in 352.10(H)" would cover box.
Also, you said 352.10(H) didn't say box, but it does say "other equipment". It further says it can't contain any devices. The OP's box has a receptacle and a receptacle is a device.
"Fat Lady" just sang the high note.
Game-Set-Match
Debate officially Lost
Good Night!
Not just yet here Bill, I have an answer for your post. Real short here, I'm tired, but 352.10(H) deals with conduit bodies not boxes. Check the definition of conduit bodies, especially the last line of the definition. They, conduit bodies are not considered boxes.
No, a fitting is always a fitting, it never magically becomes conduit when attached to one.
Does a conduit strap become a conduit when it touches conduit?
Does the box become a conduit when a conduit is attached to it?
Sorry mike it is you that has failed to prove your point.
Morning Bob, I'm here like you to learn the finer points of the NEC. I also believe that the code in a permissive code and unless something is specifically prohibitive it is complainant. So, the section we have been debating does not prohibit a fitting as part of the conduit so I don't have the burden of proof. Also a glued male connector of PVC becomes a permanent connection of the conduit.
Second this section list a fitting as complainant, "a hub." Right there is an indication that a fitting attached to a conduit or box is complainant.
Now, really, really now, don't you think what's important in this part of this section is that the connection is wrenchtight? No one has address this part of the section other then me and it seems like a position is taken because there has been a position previous taken. If true, that is sad.
Michael, you should know that most times you can't just look at one section of the code to get a definitive answer to a question.
You're mixing and matching two sections here that one doesn't go with the other, or one trumps the other.
The one for raceways being allowed to support luminaries, boxes with devices, other equipment and the one for PVC. The code for PVC doesn't allow it to support luminaries, and other equipment (boxes w/devices). It specifically says if it's not mentioned in (H) it's not permitted. It doesn't say when you glue a fitting on it that it is then allowed.
I don't know why this is so hard for you to understand!
There has been a blanket statement on this tread that "PVC is not allow to support a box." This statement was based on Section 352.10(H). Once again I disagree with the statement.
314.23(F) Raceway-Supported Enclosures, with Devices, Luminaires,
or Lampholders. An enclosure that contains a
device(s), other than splicing devices, or supports a luminaire(
s), lampholder, or other equipment and is supported
by entering raceways shall not exceed 1650 cm3 (100 in.3)
in size. It shall have threaded entries or have hubs identified
for the purpose. It shall be supported by two or more conduits
threaded wrenchtight into the enclosure or hubs. Each
conduit shall be secured within 450 mm (18 in.) of the
enclosure.
Fitting. An accessory such as a locknut, bushing, or other
part of a wiring system that is intended primarily to perform
a mechanical rather than an electrical function.
CONDUIT FITTINGS (DWTT)
USE
This category covers metallic and nonmetallic conduit fittings, such as
couplings, conduit bodies, short radius conduit bodies, expansion fittings,
locknuts and connectors for use in the assembly of nonmetallic and metallic
wiring systems. Also covered are fittings used to provide a transition
between metallic and nonmetallic wiring systems. All fittings are intended
to be installed in accordance with ANSI/NFPA 70, ??National Electrical
Code?? (NEC), and are intended for installation and use in accordance with
the following information and the limitations specified in the appropriate
conduit or tubing category.
RIGID NONMETALLIC SCHEDULE 40 AND
SCHEDULE 80 PVC CONDUIT (DZYR)
USE AND INSTALLATION
This category covers rigid nonmetallic PVC conduit (Schedule 40 and
Schedule 80), including straight conduit and elbows in trade sizes 1/2 to 6
(metric designators 16 to 155) inclusive, intended for installation as rigid
nonmetallic raceway for wire and cable in accordance with Article 352 of
ANSI/NFPA 70, ??National Electrical Code?? (NEC). This conduit is intended
for installation and use in accordance with the following information.