Charles R. Miller
Sorry I get them both and got it wrong.![]()
That's okay Dennis, I was just kidding. Besides, it was another way to shamelessly plug the magazine and my article.
IMO, to help with clarity, remove the word allowable from all ampacity statements. This word modifies the defined term ampacity in an undefined manner....
I don't care if they accept my wording; I just want the references to be clear and understandable. I would like to know other thoughts on this.
110.14(C) says nothing about continuous loads factored to 125%, nor does it mention any of the sections associated with 125% factoring.To satisfy 110.14(C) and 210.19(A)(1),
Section 110.14(C) is only for terminations. Section 210.19(A)(1) provides the wording for continuous loads. After multiplying the load by 125 percent, select a conductor from the column as determined by 110.14(C). This is also the way the calculation is performed in Example D3(a). You could select a conductor from the 90?C column (using this example), but then you will have to turn around and select the conductor from the 75?C column when determining the minimum size conductor at the overcurrrent device termination.
Your proposals are exactly what I have have been taught and have always understood is the way it is done, and states it in a way that is easier to understand than what has been in print for years.I mentioned earlier that I do not like the wording in 210.19(A)(1). It is obvious by the replies to this one question that this section is difficult to understand. Although I have a great job writing and teaching the NEC, I don't like the Code being difficult to understand. Because of this, I submitted a proposal to change the wording of this section. For this section, my proposal was accepted in principal and I like the change that was made. Here is the draft copy of this section:
210.19(A)(1) General. Branch-circuit conductors shall have an ampacity not less than the maximum load to be served. Conductors shall be sized to carry not less than the larger of (a) or (b). [ROP 2?131]
(a) Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the minimum branch-circuit conductor size shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load. [ROP 2?131]
(b) The minimum branch-circuit conductor size shall have an allowable ampacity not less than the maximum load to be served after the application of any adjustment or correction factors. [ROP 2?131]
I think the new wording is easy to understand and is what the Code is trying to say. Although it was accepted at the proposal stage, it may be rejected in the comment stage. This is what the Technical Correlating Committee (TCC) said about the proposal:
TCC Action: It was the action of the Correlating Committee that this proposal be reconsidered and correlated with the actions taken on Proposals 2-201 and 2-202. The Correlating Committee directs that the panel clarify whether the 125 percent is applied before or after the correction factors for consistency. The Correlating Committee also directs that this proposal be submitted to Code-Making Panel 6 for comment. This action will be considered as a public comment.
I submitted a similar proposals for feeder conductors in 215.2(A)(1) and, like the one for branch-circuit conductors, it was accepted in principal. I also submitted one for service conductors in 230.42 and it was rejected. Here is the response from the committee:
Panel Statement: The current text is clear that conditions of use must be considered in addition to continuous loading.
Even their statement is not clear. Do they mean to calculate the conditions of use along with the continuous loads or perform the calculations separate?
To satisfy 110.14(C) for a 75?C termination limitation, and using your example of 39A continuous load, we only have to choose the smallest size from the 75?C column of 310.15(B)(16) having an ampacity value not less than the maximum load of 39A. We do not have to factor the 39A to 125% and base the minimum size to 48A. In this case, it just happens to be an 8AWG copper conductor either way. But if we were using aluminum, 8AWG would also suffice... but not if you use 125% continuous load factoring. That would raise the minimum size for an aluminum conductor to 6AWG.
I mentioned that the overcurrent device is a factor when selecting a conductor. Multiplying the continuous loads by 125 percent and then selecting a conductor from the 75?C column is a shortcut. This shortcut is for the provision in 210.20(A).
210.20 Overcurrent Protection. Branch-circuit conductors and equipment shall be protected by overcurrent protective devices that have a rating or setting that complies with 210.20(A) through (D).
(A) Continuous and Noncontinuous Loads. Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the rating of the overcurrent device shall not be less than the noncontinuous load plus 125 percent of the continuous load.
If we are sizing aluminum conductors (as you mentioned), 8 AWG conductors would not be permitted. We can select an 8 AWG aluminum conductor because it has an allowable ampacity of 40 amperes in the 75?C column. But we must also consider 210.20(A) and 240.4. In accordance with 210.20(A), the overcurrent device must not be less than 125 percent of the continuous load. The rating of the fuse or breaker must be at least 49 amperes (39 ? 125% = 48.75 = 49). Since 49 is not a standard rating, we must use a 50-ampere fuse or breaker. Looking at the conductor we selected, it only has an allowable ampacity (out of the 75?C column) of 40 amperes. Because the 8 AWG aluminum conductor has an ampacity of 40 amperes, it must be protected with a 40 ampere overcurrent device. Therefore we must select a 6 AWG conductor, which has an ampacity of 50 amperes.
I understand it is a shortcut... and I also forgot to mention in my previous post that I'm aware this is how it is done in the D3(a) Example. It is mislabeled as pertaining to 210.19(A)(1), when it pertains to how 210.20 Overcurrent Protection (OCP) may affect the minimum conductor size determination. Nonetheless, it is not a proper application of the requirements.I mentioned that the overcurrent device is a factor when selecting a conductor. Multiplying the continuous loads by 125 percent and then selecting a conductor from the 75?C column is a shortcut. This shortcut is for the provision in 210.20(A).
I believe I have found the root of misconception. 110.14(C)(1)(b)(2) states:I mentioned that the overcurrent device is a factor when selecting a conductor. Multiplying the continuous loads by 125 percent and then selecting a conductor from the 75?C column is a shortcut. This shortcut is for the provision in 210.20(A).
Conductors with higher temperature ratings, provided
the ampacity of such conductors does not exceed the
75?C (167?F) ampacity of the conductor size used, or
up to their ampacity if the equipment is listed and identified
for use with such conductors
110.14(C)(1)(a)(3) Conductors with higher temperature ratings if the equipment is listed and identified for use with such conductors.
In a related story...I need a drink after reading all the posts. The code writer must have been an atty in a former life.
What if this load were noncontinuous? Wouldn't you apply the same correction factors (.91 and .7) to the 39 amp load? And end up with the same calculations and same conductor size (#6)? So, why use the 39 amp load instead of the 39x1.25 (48.75) for calculations for a continuous load? To me, that doesn't make sense. Maybe I'm just not looking at it the right way.
The 125% factor for continuous loads is for termination temperature and not for conductor insulation temperature. The conductor insulation can handle 100% load at its temperature rating. The overcurrent device sinks heat into the conductor - they are designed to do this, and that is why 125% of continuous load is required to be used for selecting ampacity. See the exceptions that say a breaker designed for loading to 100% can have conductors selected at 100% of continuous load. You will not find this type of breaker in typical miniature breakers installed in "load centers" so most people most of the time need to just assume they are dealing with a non-100% continuous rated breaker. Common fuses for general purposes are the same way.What if this load were noncontinuous? Wouldn't you apply the same correction factors (.91 and .7) to the 39 amp load? And end up with the same calculations and same conductor size (#6)? So, why use the 39 amp load instead of the 39x1.25 (48.75) for calculations for a continuous load? To me, that doesn't make sense. Maybe I'm just not looking at it the right way.
The reason is that you don't need to derate twice. If the continuous load is covered by the other de-rating factors then their is no issue. The correction factor for temp and wire fill automatically covers the 1.25 needed for continuous load or vice versa.
Perhaps because the determination of ratings is, shall we say, interactive over several aspects of an installation. The following is a rewrite of Post #49 changed to 39A noncontinuous load (changes indicated with red text). Take special note of the OCP rating determination.What if this load were noncontinuous? Wouldn't you apply the same correction factors (.91 and .7) to the 39 amp load? And end up with the same calculations and same conductor size (#6)? So, why use the 39 amp load instead of the 39x1.25 (48.75) for calculations for a continuous load? To me, that doesn't make sense. Maybe I'm just not looking at it the right way.