Hello friends!!
I am sizing the conduit of system with 208Y/120V, 4W, 173888 VA per phase in the facilitiy.
Load calculaiton = 173888 VA /120 V = 1449 A
Cable size = 1449/0.8= 1811 A (use NEC 310-16, 194 F, THHW Al)
No. of cable = 6 x 400 kcmil
My question is that each conduit need contain all three phases along with a neutral and all the parallel runs need to be of the same size and length. I have done as follows:
- Area of 400kcmil THHW cable: 0.6619 in^2 (from NEC2011 Table 5)
- Size of PVC conduit: 1 1/2" (from NEC2011 Table 4)
Finally, I have 6 parallel runs of 1 1/2" PVC with runs of (6) 400 kcmil THW Al coductors and (1) #3/0 AL ground conductor on each conduit. I am not qute sure this is right calculation. Also, is ground conductor like neutral conductor every conduit?
If I am wrong, would you recommend the other way.
Thanks in advance
Thanks in advance