mivey
The story of my life.Another typo...
Forgot closing parenthesis for sqrt function.
Not sure what I missed but the point is that you can't compare the vector difference with the magnitude difference. This is close:
Z = 0.4 + j0.0108 = 0.4<1.55?
Vs = 120<0?
I = 15<-30.345?
IZ = 6.0<-28.8?
Vr = Vs - IZ = 114.8<1.443?
VD = |Vs|-|Vr| = 120-114.8 = 5.2 volts /= 6.0<-28.8?
also,
Θ = Θ_I - Θ_Vr = -30.345? - 1.443? = -31.788?
Cos (Θ) = 0.85 = p.f.
Example of what?I fat-fingered this calc because I got the wrong answer for VD_exact. Since I couldn't resist, the corrected numbers for this example are:
So what scenario do the numbers represent? I see nothing which compares IR to IZ, especially showing IZ is less than IR... which is the gist of the originating question. And how does it relate to wire size?OK.
Voltage drop is IZ. Current times impedance. If R ≤ Z always, why, how, can IR ever exceed IZ?
Maybe an example of a practical application with actual numbers would be helpful.
Here R=0.4>0.34569(=Zeff)VD (approx) = I * (RcosΘ + XsinΘ) = 15 * (0.4*0.85 + 0.0108*0.52678) = 15 * Zeff = 15 * 0.34569 = 5.1853
That voltage drop is not IZ. Voltage drop is a difference in magnitudes given by |Vs|-|Vr| or by |I| * Zeff. As I stated:Example of what?
Not quite. One is a voltage vector the other is a comparison of magnitudes.Voltage drop is IZ.
You know the magnitude of I but you don't know the angle. Iterating should find the value.
It was really about the math. Another example would be:So what scenario do the numbers represent?
The gist is that Z and Zeff are two different things. One might think that vdrop = IZ but it does not since vector differences and magnitude difference are two different things. The confusion is the two different uses of the term voltage drop.I see nothing which compares IR to IZ, especially showing IZ is less than IR... which is the gist of the originating question.
I covered that in my other posts with the tables of percentages.And how does it relate to wire size?
'Z' and 'Zeff' are two different things. Exact and approximate 'Zeff' can both be less than 'R'. 'Z' can never be less than 'R'.Exact 'Z' can not be less than 'R'. But an approximate 'Z' (=RcosΘ + XsinΘ) can be.
Both vector difference and magnitude difference of two voltages point to one thing: VOLTAGE DROP, though the former is accurate and the latter is approximate.That voltage drop is not IZ. Voltage drop is a difference in magnitudes given by |Vs|-|Vr| or by |I| * Zeff. As I stated:
I also pointed out that you don't know the angle of I. Usually you have |I| |Vsource| and the power factor at the load. As I stated:
Vs - IZ = Vs - Vfeeder = Vr: 120<0? - 10<30? = 111.45<2.57?
The vector difference gives |Vs - Vr| = |IZ| = 10
The voltage drop is 120 - 111.45 = 8.55
FWIW, the numbers were for 100 feet of #12-1 at 167?F in PVC, 85% lagging p.f. load, single-phase 120 volt source.
Let them get this straight first:
|Vs - Vr| /= |Vs|-|Vr|
and the rest should take care of itself.
They are pointing to two different things. Work a few examples with various angles. It should become clear to you.Both vector difference and magnitude difference of two voltages point to one thing: VOLTAGE DROP, though the former is accurate and the latter is approximate.
No. They are pointing to two different values of the same thing i.e the voltage drop.They are pointing to two different things.
Yes. You are correct.Vector difference = Vs - Vload = 120<0? - 84.8528<-45? = 84.8528<45?
Vdrop = |Vs| - |Vload| = 120 - 84.8528 = 35.1472 volts
this is not the same as |Vs - Vload| = 84.8528 volts
Of course the values change but the concept does not. {add: see example in post #45}(1)You have taken the angle of Zfeeder to be 90. Do values change, if we take lower and more practical values for the angle of Zfeeder?
No. You are confusing the two different uses of the term 'voltage drop'.(2)No. They are pointing to two different values of the same thing i.e the voltage drop.
Then you should see they represent two different things.(3)Yes. You are correct.
One is exact and the other is an approximation but they represent the same thing: the difference in the source and load voltage vector lengths.Incidentally, '|Vs| - |Vload|' is not same as 'I*(RcosΘ + XsinΘ)' which is 'I*Zeff'.
You are correct. You mean there is no relationship between the two?You are confusing the two different uses of the term 'voltage drop'.
The vector difference tells you the voltage impressed across the feeder impedance. The magnitude difference (what we are calling 'voltage drop' per the NEC discussion) tells you the difference in the magnitude of the voltage impressed across the load vs the magnitude of the source EMF. One is a voltage vector from tail-to-tail of the source and load voltage vectors. The other is the difference in the source and load voltage vector lengths. Two different things.
NO. Take your own example at post#48.One is exact and the other is an approximation but they represent the same thing: the difference in the source and load voltage vector lengths.
The relationship is that they are based on the same two voltage vectors (V_source and V_load). However, they are two different calculations using those two vectors.You are correct. You mean there is no relationship between the two?
Yes. Nothing changes other than demonstrating that the approximation is not so good for this extreme case so the exact solution is the one that should be used. The approximate is ok when there is a small angle between the voltage vectors. This can be seen in the illustration in the IEEE red book (figure 3-11).NO. Take your own example at post#48.
Θ = 0? (the load is resistive).Since feeder impedance angle is 90 degrees, the feeder has R=0, X=1, cosΘ=0 and sinΘ=1. So feeder voltage drop= I*Zeff=84.8528*(0+1)= 84.8528 V, whereas |Vs| - |Vload| = 120 - 84.8528 = 35.1472 volts only.
The voltage drop (magnitude) is all we are concerned with, not the vector difference. The load only realizes VR without any vectorial respect to VS.That voltage drop is not IZ. Voltage drop is a difference in magnitudes given by |Vs|-|Vr| or by |I| * Zeff. As I stated:
It's a generally-accepted practice to state parameters before the exercise. When I look at the math I say to myself, what the heck is he talking about :huh:FWIW, the numbers were for 100 feet of #12-1 at 167?F in PVC, 85% lagging p.f. load, single-phase 120 volt source.
I never believed or thought Z and ZEFF were the same, nor was I aware of two different uses of the term voltage drop (for practical applications regarding wire size and circuit length). The only thing that has confused me thus far in this discussion is what I consider your divergence from the issue.The gist is that Z and Zeff are two different things. One might think that vdrop = IZ but it does not since vector differences and magnitude difference are two different things. The confusion is the two different uses of the term voltage drop.
I see no correlation. I understand that you understand your posts and how they correlate. However, readers including myself (and I consider myself fairly comprehensive) cannot always perceive another's unwritten words.I covered that in my other posts with the tables of percentages.
Okay... I'll wait and seeLet them get this straight first:
I agree. Besoeker brought up the IZ vector.The voltage drop (magnitude) is all we are concerned with, not the vector difference. The load only realizes VR without any vectorial respect to VS.
Plenty of room in the Q&A session. Sometimes I just type as I think. Oh well.It's a generally-accepted practice to state parameters before the exercise. When I look at the math I say to myself, what the heck is he talking about :huh:
I know you didn't but others have.I never believed or thought Z and ZEFF were the same
The vector difference is also called voltage drop, but in a different context. That is the IZ reference.nor was I aware of two different uses of the term voltage drop (for practical applications regarding wire size and circuit length).
Then I guess you did not follow the other poster's questions about Z can't be less than R and that voltage drop = IZThe only thing that has confused me thus far in this discussion is what I consider your divergence from the issue.
The list of percentages I gave were directly related to what you said about R & effective Z. The other had nothing to do with what you said as you were not discussing Z instead of Zeff.I see no correlation.
I don't believe he did. Yes he brought up "IZ", but in the context of discussion I do not think he meant vectorial IZ... but rather E=IR (magnitude only) transformed to VD=IZEFF for the purpose at hand. Once you brought up vector Z, the discussion drifted.... Besoeker brought up the IZ vector.
I will simply refer you to post #15:I don't believe he did. Yes he brought up "IZ", but in the context of discussion I do not think he meant vectorial IZ... but rather E=IR (magnitude only) transformed to VD=IZEFF for the purpose at hand. Once you brought up vector Z, the discussion drifted.
That my friend is vector Z, not Zeff. That is also the significance of saying that Z can't be less than R and that voltage drop = I * Z (not Z of the Zeff kind).Z=(R2+X2)1/2
That point presents the point well and deserves merit.One gives you the voltage dropped across the wires while the other gives you the difference in the voltage seen by the load.
See it as you will... but I've yet to see him indicate any value in true vector form in this discussion. However, I didn't see your response to his post as a divergent.I will simply refer you to post #15:
Again no indication of vector values.OK.
Now can we get back on track? The objective was and remains to show an instance of IR > IZEFF, where IZEFF = VD = |VS| - |VR|.