fisherelectric
- Northern Va
I have been asked to design the service for a big house. Service is to be 800 amps. The CT cabinet is to be located in a small building about 50' from the main house. There will also be a large detached garage/apartment about 100' away that will require 200 amps. They want to install the service equipment in the small building with the CT cabinet rather than in the house. My first thought was to use a 6 breaker I-Line panelboard as the service with 4 200 amp breakers and run 3 sets of 250 with #4 equipment ground into the house and one set to the garage. But after looking at 225.30 I have doubts this would be compliant and I would have to run 1 600 amp feeder to the house, set a trough and feed disconnects that way.
However, if I could talk them into putting the service in the house rather than out next to the CT cabinet, according to 230.4 excep #2 I could run 4 sets of 200 amp service entrance conductors directly from the CT cabinet into the house into disconnects and then feed the garage from there. That would seem to be a lot more cost effective.
So if they stick to their plan of putting the service equipment next to the CT cabinet I would have to install a 600 amp disconnect for the house and a 200 amp disconnect for the garage at the CT cabinet in addition to disconnects at both the house and garage.
Any thoughts would be appreciated.