Isn't this a bad idea?  The current is attempting to return to the POCO transformer and will find a path through the earth.  What if that path is through the neighbors nearby pool?
Well not really in the sense that a pool over 26 feet away from the current injection point would most likely not see any voltage rise, this distance would increase if the soil was of a poor conductive material such as sand, as the higher the soil resistance the larger the SOI.
One of the biggest myths is that stray voltage can travel far in the Earth, in fact this is not true, current can travel around the world but to measure any voltage would be like putting 1 amp on a 10' length of 2000 kcmil then placing a volt meter with the leads 1" apart somewhere in the middle, once we have reached the SOI of the current injection point which is about 25' the 3 dimensional parallel paths through the earth are so many the the resistance is so low that there is virtually no voltage drop.
Even current outside of the SOI is almost undetectable since you are only measuring a very extremely small section of all the parallel paths that the current has taken.
When the Navy tried to use ELF 76hz to send messages to their submarines they had to build a transmitter that had an antenna 32 miles long which was a fraction of the 2268.27 mile long wave length of 76hz, it took a tremendous amount of power just to send a a few watts of transmitted power, this was all started when it was discovered that we could detect the 50hz power systems from Europe with a highly amplified spectrum analyzer, but since this current was so spread out across the globe it was very weak, also the transmitter had to use very high resistance soil which they found at Republic, Michigan in the Upper Peninsula and at Clam Lake, Wisconsin, both were abandon around 2004, of course it was a one way communications since the subs had no way to supply that kind of power, but the problem wasn't that the current didn't go all around the earth, it was that by the time it took all the parallel paths around the globe and through it the signal was so weak it was too hard to receive it, the amount of power it took was never disclosed, a friend of mine who worked on the Clam Lake WI. one said they had a very large dedicated power plant to just supply power for the transmitter, so I can imagine the amount of amps they had to inject into the earth.
generally stray current is carried onto the property through a conductor such as the service neutral, it may be caused by a fault miles down the road but its not injected into the earth that far away, it comes down the road on the utility's MGN which is bonded to the service neutral that is raised above earth potential, earth is never raised above the neutral potential unless it is a very close event, it can also be brought in through water and gas lines or other conductive pathways, but earth has a greater ability to stay at it's reference zero volts then any conductor can raise it above it if there is any distances from the last point of electrode connection.