marley120993
 - milford ct
can you install a20amp gfci on a 15 a circuit for a garbage disposal
			Uhhhh, I think not Rob. Take a look at the table I mention earlier. For a 15 amp circuit, you can't have outlets rated above 15 amps. Perhaps you are thinking about having a pair of 15 amp receptacles on a 20 amp circuit?
Your table is for 2 or more receptacles.
(3) Receptacle Ratings. Where connected to a branch
circuit supplying two or more receptacles or outlets, re-
ceptacle ratings shall conform to the values listed in
Table 210.21(B)(3), or, where rated higher than 50 am-
peres, the receptacle rating shall not be less than the
branch-circuit rating.
The charging statement for the use of Table 210.21(B)(3) is in 210.21(B)(3) and says:Disagree. It is a "Table 210.21(B)(3) Receptacle Ratings for Various Size
Circuits"
(3) Receptacle Ratings. Where connected to a branch circuit supplying two or more receptacles or outlets, receptacle ratings shall conform to the values listed in Table 210.21(B)(3), or, where rated higher than 50 amperes, the receptacle rating shall not be less than the branch-circuit rating.
The table does not permit a single 15 amp receptacle on a 20 amp branch circuit. 210.21(B)(1) permits a single 20 amp receptacle on a 15 amp circuit. If Table 210.15(B)(3) applied to single receptacles it would be in conflict with the rule in 210.21(B)(1).The table applies to single receptacles because it allows me to place a single 15 AMP rec. on a 20 AMP circuit and prohibits me from putting a single 20 AMP rec. on a 15 AMP circuit.
(B) Receptacles.
What are you trying to tell me with this post? I don't understand.He has a disposal and I'll bet that it has a switch.
I think he mistakenly believes a switch is an outlet.What are you trying to tell me with this post? I don't understand.
(B) Receptacles.
You have it backwards. And the table does not apply to single receptacles.
Roger
I know you guys know what an outlet is but:
Outlet. A point on the wiring system at which current is
taken to supply utilization equipment.
Branch circuit goes to the switch outlet then the receptacle outlet I have two or more outlets.
210.21(B)(3),