2-97 Log #2732 NEC-P02 Final Action: Reject
(210.12(A) Exception (New) )
________________________________________________________________
Submitter: Robert Meier, Norwood, NJ
Recommendation: Add text to read as follows:
210.12(A) Dwelling Units. All 120-volt, single phase, 15- and 20-ampere
branch circuits supplying outlets installed in dwelling unit family rooms, dining
rooms, living room, parlors, libraries, dens, bedrooms, sunrooms, recreation
rooms, closets, hallways, or similar rooms or areas shall be protected by a
listed arc-fault circuit interrupter, combination-type, installed to provide
protection of the branch circuit.
Exception: Lighted switches are not required to comply with this section.
Substantiation: A lighted switch, by definition in Article 100 is an outlet.
Being such, and when installed in one the areas requiring AFCI protection, the
switch itself would require AFCI protection even if it were controlling
something in an area that does not require AFCI protection. For example a
lighted switch in a dwelling bedroom would require AFCI protection even if it
controlled a portion of as circuit that does not require AFCI protection such as
an outdoor light. By adding this exception it will clarify that this switch,
although an outlet by definition, does not require AFCI protection,
Panel Meeting Action: Reject
Panel Statement: The panel has included ?devices? in the requirement which
will clear up confusion regarding lighted switches.
See the panel action and statement on Proposal 2-85.