Yes we do and a switch is not an outlet, it is a device and the NEC makes that clear.I know you guys know what an outlet is but:
The NEC took pains to specifically define what items are to be considered "outlets", as follows.
Lighting Outlet. An outlet intended for the direct connection of a lampholder or luminaire
Outlet. A point on the wiring system at which current is taken to supply utilization equipment.
Power Outlet. An enclosed assembly that may include receptacles, circuit breakers, fuseholders, fused switches, buses, and watt-hour meter mounting means; intended to supply and control power to mobile homes, recreational vehicles, park trailers, or boats or to serve as a means for distributing power required to operate mobile or temporarily installed equipment.
Receptacle Outlet. An outlet where one or more receptacles are installed.
Receptacle. A receptacle is a contact device installed at the outlet for the connection of an attachment plug. A single receptacle is a single contact device with no other contact device on the same yoke. A multiple receptacle is two or more contact devices on the same yoke.
Now notice there is no such animal as a Switch Outlet.
A switch simply connects wires the same as a wire nut does only easier.Switch, Bypass Isolation. A manually operated device used in conjunction with a transfer switch to provide a means of directly connecting load conductors to a power source and of disconnecting the transfer switch.
Switch, General-Use. A switch intended for use in general distribution and branch circuits. It is rated in amperes, and it is capable of interrupting its rated current at its rated voltage.
Switch, General-Use Snap. A form of general-use switch constructed so that it can be installed in device boxes or on box covers, or otherwise used in conjunction with wiring systems recognized by this Code.
Switch, Isolating. A switch intended for isolating an electrical circuit from the source of power. It has no interrupting rating, and it is intended to be operated only after the circuit has been opened by some other means.
Switch, Motor-Circuit. A switch rated in horsepower that is capable of interrupting the maximum operating overload current of a motor of the same horsepower rating as the switch at the rated voltage.
Switch, Transfer. An automatic or nonautomatic device for transferring one or more load conductor connections from one power source to another.
And what is your point?Outlet. A point on the wiring system at which current is
Branch circuit goes to the switch outlet then the receptacle outlet I have two or more outlets.
(3) Receptacle Ratings. Where connected to a branch circuit
supplying two or more receptacles or outlets, receptacle
ratings shall conform to the values listed in Table
210.21(B)(3),