15 amp circiuts
Uhhhh, I think not Rob. Take a look at the table I mention earlier. For a 15 amp circuit, you can't have outlets rated above 15 amps. Perhaps you are thinking about having a pair of 15 amp receptacles on a 20 amp circuit?
Your table is for 2 or more receptacles.
You didn't read the section above the table.
(3) Receptacle Ratings. Where connected to a branch
circuit supplying two or more receptacles or outlets, re-
ceptacle ratings shall conform to the values listed in
Table 210.21(B)(3),
or, where rated higher than 50 am-
peres, the receptacle rating shall not be less than the
branch-circuit rating.
Disagree. It is a "Table 210.21(B)(3) Receptacle Ratings for Various Size
Circuits"
The charging statement for the use of Table 210.21(B)(3) is in 210.21(B)(3) and says:
(3) Receptacle Ratings. Where connected to a branch circuit supplying two or more receptacles or outlets, receptacle ratings shall conform to the values listed in Table 210.21(B)(3), or, where rated higher than 50 amperes, the receptacle rating shall not be less than the branch-circuit rating.
The table applies to single receptacles because it allows me to place a single 15 AMP rec. on a 20 AMP circuit and prohibits me from putting a single 20 AMP rec. on a 15 AMP circuit.
(B) Receptacles.
(B) Receptacles.
The table does not permit a single 15 amp receptacle on a 20 amp branch circuit. 210.21(B)(1) permits a single 20 amp receptacle on a 15 amp circuit. If Table 210.15(B)(3) applied to single receptacles it would be in conflict with the rule in 210.21(B)(1).
marley120993, perhaps you could let us know whether the circuit in question supplies loads other than the garbage disposal, and whether the receptacle you intend to install is a simplex or a duplex?
(B) Receptacles.
You have it backwards. And the table does not apply to single receptacles.
Do you need a GFCI on a disposal anyway? It's under the counter and most of them are switched above the counter.
I would think ( without actually knowing ) you could put a higher rated recep on a lower rated circuit. Not on stuff like 30A twist locks , but regular receps? why not?
Just don't go the other way and use a 15 as the sole recep on a 20a circuit.
I as confused by some of the answers you got honestly.
What are you trying to tell me with this post? I don't understand.
I think he mistakenly believes a switch is an outlet.
Roger
I know you guys know what an outlet is but:
Outlet. A point on the wiring system at which current is
taken to supply utilization equipment.
Branch circuit goes to the switch outlet then the receptacle outlet I have two or more outlets.
210.21(B)(3),
210.21(B)(3),
In what you described, the switch is not an outlet, the receptacle is. The current is supplied to the utilization equipment at the receptacle, it only passes through the switch.