Hello everyone.
Working on a project with a 800A cummins transfer switch. The transfer switch was actually provided by the owner and given to the electrician to install. The problem is that our drawings indicated (2) sets of #600 kcmil but the owner ordered a the wrong lugs for it. The lugs can not accept the #600 wire because the lugs are only meant to accept (4) sets of #400 wire (max). Cummins claims they cannot send a new set of lugs because it would void the UL listing on the equipment.
The (2) sets of #600 wire is already pulled and into place and has been there well before the transfer switch was on site.
Question:
Would it be permissible to make a tap within the transfer switch and change the conductors to (4) sets of #3/0? The inside of the ATS is pretty large and there seems to be ample room in there.
Question: