Plywood backplate inside 480 volt load center?
cliffer1
New member
Has anyone come across a load center cabinet with the breakers, contactor, etc. mounted to a plywood panel inside? I have seen it with low voltage lights but never 480 volts.
Can you point me to an NEC reference for this being acceptable?
The load center controls roadway lighting for D.O.T. street lights and high-mast towers.
Thanks!
Thanks!
I don't know the code reference, or if something like this is even within the code's jurisdiction, but I have seen it in the field.
DOT can pretty much do as they please. Governmental agencies are usually exempt from the pesky rules that apply to the rest of us.
My guess is that there is no rule on what these backplanes are made of to be found in the code.
In Florida a unit of state, county or city government does have to comply with code.
However, highways, bridges and things accessory thereto are exempt, and that exemption does include traffic signals and highway lighting.
OP needs to find out if job specs or the FDOT construction manual compel compliance with the NEC because statutorily it does not.
Only thing I know that comes close is the restriction on setting switchboards on wooden floors.
Maybe the distinction here is that while a wooden backboard would burn, it still wouldn't permit flame-spread outside the enclosure.