- Massachusetts
If supervised location under engineering supervision
most cases I would guess
Well if you are playing that card all bets are off.
I know many engineers believe they can supersede code ampacities with their own calculations as prescribed by 310.15(A)(1) and (C), or 310.60(B) and (C). However, that only applies to Article 310 ampacities. It does not apply to termination temperature limitations imposed under either 110.14(C) or 110.40.Well if you are playing that card all bets are off.
And all I am asking is for you to link us to the manufacturer's documentation which clearly states that. Then it qualifies as UOI...Not sure if I am the one who missed it lol
The mv SW without question is rated for use with 105 cable
105 cable does not de-rated to use it
No, you cannot. Article 110 specifies the use of the appropriate Table. No option for engineering supervision.If you can pick your own ampacity of the cable you can get around the termination temps.
Correct?
In other words I just claim the cable is rated X amps at 75C.
Correct?
What about this:No such 125% continuous factoring requirement for MV.
2011 NEC said:215.2(B) Feeders over 600 Volts [ . . . ]
(2) Feeders Supplying Transformers and Utilization Equipment. The ampacity of feeders supplying a combination of transformers and utilization equipment shall not be less than the sum of the nameplate ratings of the transformers and 125 percent of the designed potential load of the utilization equipment that will be operated simultaneously.
The "will be..." lets it be highly subjective. Not the same as "may be..."What about this:
...125 percent of the designed potential load of the utilization equipment that will be operated simultaneously.
Seems like all non-transformer loads get 125%, unless you go to part (3) Supervised Installations.