Are we seeing NM cable zip tied to the plumbing stack?
To pile it on here-
The hot going to the left hand lug on brkr looks like it might need some tape too.![]()
What about the two single # 6?? wire entering the lefthand bottom
or
no white tape on upper incoming feeder?
or
nice grounding bushing...is it tied to ground??
If any of those are equipment grounding conductors and larger then #6 then yes. If EGC are #6 or smaller then the insulation must be green.Shouldn't there be some green tape in there somewhere too?
The conductors to the right could be GEC's. Can't see whether they are terminated. If they are GEC's there is definitely a bonding issue.There are also two conductors not in a raceway entering from lower right and a black sheathed cable to the left of the white pvc. They don't seem to do anything.
Can't say whether that is wrong or not. It is commonplace to use wood screws in wood masonry plugs. It's quite similar to using a plastic anchor.And it looks like they used wood screws to mount the enclosure to brick.
Let's cut out the sarcasm.Does this thing have a cover, or is it a live front in its natural form?
What kind of screws should one use - especially if there are plastic anchors in the brick? Plastic screws?And it looks like they used wood screws to mount the enclosure to brick.
Does this thing have a cover, or is it a live front in its natural form?
What kind of screws should one use - especially if there are plastic anchors in the brick? Plastic screws?
Some of those red bricks are soft enough a wood screw may go in and hold fairly well - especially if you drilled a pilot hole first.
Hopefully it has a cover, but the main question concerning the open KO is a little hard to show and ask about with the cover on.
Only ones around here that'd be that soft are pre-fired bricks, i.e. a not-yet-brick brick. :blink:...
Some of those red bricks are soft enough a wood screw may go in and hold fairly well - especially if you drilled a pilot hole first.
...
I'd call you on the ko seal, even though it's on a brick wall you never know what might end up under that panel and when the sparks start flying they could light something on fire.
Now don't take it that I'm a hard nosed inspector, but I have a reputation even among my own inspectors that I can find the only missing ko seal in a building of any size.