Phil Corso
- Boca Raton, Fl, USA
Gentlepeople… a reminder:
Here is the solution using my Gi.Fi.E.S. (Pronounced Jiffy’s) method:
Given:
o Hi-Leg distribution system: Vrw = 240<0⁰; Vbr = 240<-120⁰; Vwb = 240<+120⁰;
o Line-currents to load bus: Ib = 294A; Ir = 256A; Iw = 341A.
o Neutral-current: In = 0A, thus supply can be considered as typ 3-ph, Delta!
o Xfmr capacities: Tbr = 50kVA; Trw = 75kVA; Twb = 50kVA.
Not Given:
o Any info on Load-type.
o Any info on Load phase-currents.
o Any info on Load PF(s).
o Any info on Xfmr parameters like, %Imp; X/R; V-Reg.
Find:
o Which of the 3 Xfmrs is overloaded, meaning determine kVA generated, or produced in each.
Equations:
Solution:
Phil
Given:
Not Given:
Find:
Equations:
Solution:
Phil