gadfly56
Senior Member
- Location
- New Jersey
- Occupation
- Professional Engineer, Fire & Life Safety
Ooooh, matrix math! Careful, your geek is showing!
This is convincing. I'd like to see how I can arrive at that identity matrix though. I know it's a bit extra writing, but do you mind posting the steps. it will help be grasp it better.
Ooooh, matrix math! Careful, your geek is showing!
I did it thru inspection
ia = -1 iac + 0 icb + 1 iba
so first row = [-1 0 1]
and so on
the inverse is indeterminate
So no go
took another approach (matrix but simpler)
think I got it
using my conventions from above
and Ia = 300, Ib = 275 and Ic = 250 at 0, 120, 240 deg respectively
I get iac = 161 ang -51
a few others had a solution
I'll post mine after they share lol
GentlePeople...
Wrong, wrong, wrong!
One doesn't need to know more than arithmetic! Hogwash to identity matrix, and xfmr %Z! And, more importantly ignore the Load!
Will reveal answer tomorrow... must first check with my lawyer to insure I'm not releasing proprietary info!
Phil
GentlePeople...
Wrong, wrong, wrong!
One doesn't need to know more than arithmetic! Hogwash to identity matrix, and xfmr %Z! And, more importantly ignore the Load!
Will reveal answer tomorrow... must first check with my lawyer to insure I'm not releasing proprietary info!
Phil
Well this is the most progress so far.
GentlePeople...
Wrong, wrong, wrong!
One doesn't need to know more than arithmetic! Hogwash to identity matrix, and xfmr %Z! And, more importantly ignore the Load!
Will reveal answer tomorrow... must first check with my lawyer to insure I'm not releasing proprietary info!
Phil
I took it to mean he has a patent, top secret information, or even something that may effect national security on how to calculate this and only he/his company has rights to use those methods.:huh:Thanks
Don't get arrested!
Please do the math here: Page 108 to 110 of this reference LINKGood day, all.
I require assistance in determining how to calculate whether one transformer in a three phase star/delta bank is overloaded based on the line current on the delta side (load side).
I know that I can simply have a lineman take readings at the transformer at the X1 or X3 terminals, but I need to know how to calculate it.
So for example, let's say that the bank consists of 50,75, 50 kVA transformers, and the line currents on the delta (load) side are taken to be 256A, 294A, 341A, how do I work out the phase currents in the delta side of the transformer?
View attachment 15212
Thank you in advance.
checked my math, made a small math error
all 3 phases offset by -67 deg to normalize ph at 0
assumed V = 240
iab = 160/0...... 38.5 kva
ibc = 185/120...... 44.4 kva
ica = 178/-140...... 42.7 kva
curious what others come up with
the sequence varies from my previous because I oriented ph seq differently
the avg of the above Ph currents x sqrt3 = 301 A
the avg of the measured line currents = 297 A
Ladies and Gentlemen,
Although InJunEar's calculation of the load's phase-currents is an incorrect approach, he's on to something!
Now, calculate total kVA using the average of Line-currents, Ib, Ir, Iw!
Phil
So far you've been all hat and no cattle. You said you were going to share some super duper analytical method. Time to pony up before others here head back to the chalk board.
Your phase vectors aren't adding up to the line vectors. For example, should work out that Iab - Ica = Iachecked my math, made a small math error
all 3 phases offset by -67 deg to normalize ph at 0
assumed V = 240
iab = 160/0...... 38.5 kva
ibc = 185/120...... 44.4 kva
ica = 178/-140...... 42.7 kva
curious what others come up with
the sequence varies from my previous because I oriented ph seq differently
the avg of the above Ph currents x sqrt3 = 301 A
the avg of the measured line currents = 297 A