Your assumption about the sum of the delta currents being zero in incorrect
there is a current
KCL is for a node not a loop
the xmfr Z is moot and not a factor, unless you assume a balanced load, which it is not
the Z is unknown and is what determines line current
in adfition the Z %pu has no phase or complex component
there are 6 unknowns
3 x phase i mag
3 x phase i ang
only 3 knowns
3 x line i
not sure the assumtion that the phase v's are balanced is valid in this caee
Ans.1 : In fact, I did consider those currents! Those values were used, multiplied with the inverted matrix to get the phase currents. Please see the vectorial addition of the resulting phase currents in relation to the line current: I've cut and pasted from the worksheet that I did, here:TopGone...
Several questions::
1) OP said 256, 294, 341 for Ia, Ib, Ic, so why did you ignore those values?
2) Op said source was hi-leg, so how did you come up with 3-ph, 208?
3) Assuming ph sequence is A-B-C, then (usually) Ia is the vectoral sum of Iab + Ica => Vab/Za + Vca/Zb, then how did you derive Za anc Zc?
Phil
InJunEar,
So... your one of those "Damn the torpedoes, full speed ahead" guys!
You ignored advice from your prof, (50 yrs, industry/Academic) and now me, (63 yrs, Industry/Gov/Academic)!
Phil
InJunEar,
Phil
TopGone, InJunEar...
Perhaps the following examples will show you the error of your way(s):
1) Given: 1-phase circuit; V= 117V @ 127 Deg; Line current = 56.3A! What is the magnitude and nature of the load?
2) Given: All of the above, but an installed Wattmeter indicates 1812W? What is the magnitude and nature of the load?
Regards, Phil Corso
No one familiar with FEA? (finite element analysis)
Easy, just draw the circuit and insert values, answer spits out for even the most complicated VFD circuit.
'student/eval version' good for simple power problems like this;
http://www.orcad.com/products/orcad-lite-overview?gclid=COG-5_yY7s0CFYVrfgod8eUPmA
Have used a similar type FEA since 1988, absolutely indispensable for circuit design, esp power electronic circuits such as vfd design.