teh_engineer
- Baltimore, MD
Good morning,
I'm working on a roadway project, which is new territory for me (I only have experience with projects with runs no greater than maybe 1000') , and have a question regarding voltage drops, specifically over extremely long distances.
This project has one power distribution cabinet for license plate readers &c well over 6500' away from the source distribution point (highway administration building), which is 3P, 277/480V (I was told that there was no MV 4160V available, and there aren't any usable utility poles nearby). I'm calculating about (6) 600kcmil to just barely achieve 3% drop for a 200A panel 6500' away, which seems like a ludicrous amount of material and unfeasible from a practical standpoint.
My question is: are there any special modifications to the voltage drop formula for long distances?
If not, is there any equipment that is typical for these sorts of installations that will help mitigate or correct the voltage drop, e.g. voltage regulators or buck boost transformers every x feet? I'm thinking that there are practical limitations as well, e.g. the length of cable spools and maximum reasonable pull distance
Thanks in advance
Thanks in advance