See 440.4It is used by the manufacturer to calculate MOCP and MCA as required by the applicable standard not the NEC.
I've seen it. I guess the nec needs to update their code section to comply with the current ashrea standards for manufacturers.See 440.4
ASHRAE is irrelevant to the electrical circuiting and protection of the unit. The MCA is required to be per the NEC. The MOCP cannot be larger than allowed by the NEC.I've seen it. I guess the nec needs to update their code section to comply with the current ashrea standards for manufacturers.
The MCA has not been calculated according to the NEC since 1976. That is when ashrea changed to RLA on compressors. RLA is a percentage of MCA so how do you use RLA to calculate MCA? MCA divided by either 1.56 or 1.44 (depending on compressor manufacturer) equals RLA.ASHRAE is irrelevant to the electrical circuiting and protection of the unit. The MCA is required to be per the NEC. The MOCP cannot be larger than allowed by the NEC.
See 440.33The MCA has not been calculated according to the NEC since 1976. That is when ashrea changed to RLA on compressors. RLA is a percentage of MCA so how do you use RLA to calculate MCA? MCA divided by either 1.56 or 1.44 (depending on compressor manufacturer) equals RLA.
Seen it, doesn't answer my question. And I should add inverter compressors don't come anywhere close to NEC calculations.See 440.33
My bad there are two mca's. Minimum Circuit Amps and Maximum Compressor Amps. If you use RLA to calculate Minimum Circuit Amps it may be close on ac volt compressors but it is almost never exact. It is not close on inverter compressors.Minimum circuit conductor ampacity equals the sum of the rla of the compressor(s) and the fla of the other motor(s) plus 25% of the largest motor.
The rla is not a specific ratio of the minimum circuit ampacity. It can't be if the mca involves other motors in addition to the compressors, or if it involves multiple compressors.
Its exact with either type of compressor.I should also add the NEC has zero authority over manufacturers
According to the NEC but not to the manufacturers. I haven't come across any in a long time.Its exact with either type of compressor.
The NEC cannot dictate anything to manufacturers. Ashrea has standards that manufacturers follow. Units are tested and listed to ashrea standards, not NEC code. Electrical connections to those units are governed by the local AHJ. If the NEC is the code they follow then electrical connections to the units should use the MCA and MOCP given
That is false. The NEC can not dictate to anyone, they are nothing more than a think tank that tries to sell their ideas to AHJ's. Only AHJ's have any authority, the NEC does not.The NEC does dictate to the manufacturers. The MCA and MOCP from the manufacturer cannot be less than (mca) nor greater than (mocp) the NEC requirements.
That is absolutely false. The NEC writes code. The AHJ can adopt that code, change that code, completely ignore that code, or adopt another code. The NEC is purely an idea or suggestion until an AHJ adopts it. There is no national electrical code in the USA. Ashrea is a national standard that is followed by all USA HVAC manufacturers.The is false. The NEC makes the dictates, specifically mandatory rules. The AHJ has the responsibility for enforcement of these rules.
ASHREA is a society of engineers that develop national standards for manufacturers that all us HVAC manufacturers follow. Their standards are adopted by ANSI and many are used worldwide.This is false. ASHRAE is a society of engineers, not a national standard.
Since all US manufacturers us the same standards do you know any jurisdiction that is going to tell their people they can not have AC or heat because the equipment does not meet the NEC's antiquated code?True, but most jurisdictions adopt the NEC wholesale or make small modifications. The track record of jurisdictions adopting all/most of the NEC is such that pretty much whatever the NEC says the manufacturer will be forced to follow (if they want to sell their equipment there which they will). Do you know of any jurisdictions that add "HVAC equipment" to 90.2(B)?
Yes pretty much all of them. Just look at all the dumb things they put in the NEC and how many jurisdictions just blindly adopt it.Since all US manufacturers us the same standards do you know any jurisdiction that is going to tell their people they can not have AC or heat because the equipment does not meet the NEC's antiquated code?