and Do not use the GES in lieu of separate ground rods for your fencer. Keep both well separated.
I think this is key.
I never had a problem with electric fences very close to the water fountains, but fence chargers always had their own ground rod.
and Do not use the GES in lieu of separate ground rods for your fencer. Keep both well separated.
More evidence that there is elevated voltage on the EGC wherever you are plugging that cord into.Thanks for the help. Here is an update:
If a tester shows a good ground, but it could be a bootleg how does one really know if the ground is up to snuff. Visual? We are going up date the panel in the shop with a breaker box and will run new wires to the outlets and see if that solves the problem. He did call me and said the smaller cord does not have a ground pin. This is the cord that removes the voltage to ground whereas the newer cord with a ground pin brings back the voltage to ground. The water tank is plastic and the heater is new out of the box.
Yep, look at pretty much every place the could be a connection to see if there is and should be/etc; that is, check the entire system.If a tester shows a good ground, but it could be a bootleg how does one really know if the ground is up to snuff. Visual?
Aha! Comparing apples and grapefruit. (Never completely trust what the customer says, lots of threads here about that.)He did call me and said the smaller cord does not have a ground pin.
If there is rise in voltage on the EGC a GFCI will not respond to it.Yep, look at pretty much every place the could be a connection to see if there is and should be/etc; that is, check the entire system.
Aha! Comparing apples and grapefruit. (Never completely trust what the customer says, lots of threads here about that.)
There's still the question of a ground fault on the heater; if nothing else, try it on a gfci outlet when it's in the water and see if that trips. AFAIK that's still too much current for around cattle, but it's easy to do.
You have that backwards. He said the 14 cord had no ground pin and that when it was used, the voltage problem went away.If the cord with the ground conductor always solves it, measuring the current in that ground wire may give you a clue as to the root cause.
I understood that it was on again, off again with either cord.You have that backwards. He said the 14 cord had no ground pin and that when it was used, the voltage problem went away.
He chimed in later with additional info and said the cord being used when there was no stay voltages present had missing EGC pin. Tells me right there the stray voltage is originating from EGC, but exactly where (somewhere upstream from where it is plugged in) is yet unknown.I understood that it was on again, off again with either cord.
Your take would sure point to a neutral problem.
Some of those types will freeze if there isn’t enough water usage.If you or your customer absolutely cannot find the problem, then this is the solution...........
![]()
Horse Drinker | Bar Bar A | Automatic Waterer
Looking for a non-electric automatic waterer for your pets or livestock? Visit our website or call Horse Drinker @ 866-259-8047 today!www.horsedrinker.com
No freezing, no electricity involved. Oh yes.........just don't plumb it with metal piping.
To the OP, IMO this ^ is the very next thing to do. If you need assistance in methodology of how to do this, ask and I'm sure you will get answers.Check for bad neutral supplying the shop, or elsewhere in the distribution to the shop. Any rise of volts to ground on the supply neutral will raise all EGC's to ground that are connected downstream from it.
If he drove it next to the watering tank (instead of at the source) and bonded the water to the ground rod it might be a different outcome.I would not eliminate the possibility of NEV but I would be checking out all the wiring and meggering the feeder first. One thing for sure is that driving a ground rod was a complete waste of time and resources as it always is.
PoCo problem to winI'll place my bets accordingly,
Wiring problem local to the ranch to win, alien abduction of electrons to place, and poco problem to show.