- NE Nebraska
- EC
The problem is the insulation rating in the motor. If you are running it at 240 instead of 480 your troubles will be less.UPDATE:
So I got the ABB drive and got intouch with the motor manufacturer as they still make this motor.
And they said that since the motor is from the 70's its too old to run on a VFD and presumably I should buy a new motor.
Now my plan is not to use any VFD features, just as a phase converter, set it at 1200 RPM.
I plan to have it be triggered with an icecube relay, where the coil of the icecube is powered by the existing 120V controls.
Any thoughts/ experience on using a VFD with an old motor, like 40 years old?
Thanks all
Also as mentioned a line reactor between the drive and the motor will lessen the peaks that are going to be damaging to the motor insulation. This possibly not even much concern for 240 volt operation but likely would be a must for 480 volt operation.