Last old motor at 480 we had fail was shorted windings. Load reactor and within 30. Key word is 'old'. Still 100hp.
Have a 100 HP motor at one client that is probably from late 1980's or early 90's that we put on a VFD sometime in last 5 years. ~100 feet from drive to motor. Put reactor on drive output right away on that one, no problems yet.
Part of same process in that plant is a 50 HP motor that we put on a VFD maybe 15 years ago. Didn't know so much about drives back then and issues with older motors. Had to rewind that motor about once a year after putting it on the drive. We did succeed with part of our goal of slowing that machine down as we could run at slower speed but adjust other items and still get the right consistency out of production line - the main reward was more life on some components, and probably used less power though that wasn't as obvious without monitoring that machine's power consumption.
But kind of wiped out the rewards when needing to rewind the motor about once a year. Finally convinced owners to purchase a new motor that is rated for use with VFD's as well as with a separately powered cooling fan (we run this thing down to about 30 Hz at times but at/near full load current so between poor cooling and IGBT issues the motor wasn't lasting all that long. Only thing we have done to that motor since then was to replace bearings in the cooling fan a time or two - learned the hard way to make sure to have proper overload on that tiny three phase fan motor so that it will catch bearing failure before burning out motor windings. Think it was only like 1/4 HP @ 480 three phase, tenths of amps on motor overload setting are critical on that one.
Also learned hard way on that same machine at one time that if you bypass oil pressure switch because it failed, make sure to actually replace it ASAP. it went bypassed for maybe years, then ran out of oil one time and caused lots of rework to be needed.