Another C10
Electrical Contractor 1987 - present
- Southern Cal
- Electrician NEC 2020
250.8 (B) not permitted, connections, devices or fitting that depend solely on solder.the requirement to use the metal under ground water pipe as a grounding electrode.
250.53 (2) Supplemental electrode required as noted in
250.52 (A)(2)
I suppose one is at the mercy of the inspector, I'd argue the point of 250.8 (B) or 250.53 (2)
California requires 2 grounding rods, If I were to try to utilizes the water system as my earth ground I'd fail inspection.