Patpowers
- Mississippi
- Electrician
Receptacle.
A contact device installed at the outlet for the connection of an attachment plug, or for the direct connection of electrical utilization equipment designed to mate with the corresponding contact device. A single receptacle is a single contact device with no other contact device on the same yoke or strap. A multiple receptacle is two or more contact devices on the same yoke or strap. (CMP-18)
Outlet
A point on the wiring system at which current is taken to supply utilization equipment. (CMP-1)The term outlet is frequently misused to refer to receptacles. Although receptacle outlets are outlets, not all outlets are receptacle outlets. Other common examples of outlets include appliance outlets, lighting outlets, and smoke alarm outlets.
These are the definitions from the 2020 code book. 250.140 and 250.134 specifically use outlet not receptacle. 250.138 is not satisfied by 250.140. 250.140 exception does not declare that the grounded conductor is now an EGC, it only states that it is allowed to be bonded to the non current carrying metal parts.
250.138 has no exception to the EGC
250.134 does reference the 250.140, but only outlet not receptacle.
Outlet