Alwayslearningelec
- NJ
- Estimator
Sorry for new thread but other one got a little messy and loads/calcs changed.
I think this is a little cleaner and easier to follow.
Following loads to be fed:
(3) single phase 120/208v panels.
(1) w/ 125A MCB
(2) w/ 60A MCB
Material I will use for these power requirements.
3P-70A breaker in existing 277/480v panel. This will feed 3P 45kva xfrmr.
I will run 3/c #3 aluminum MC to the primary side of 45kvs xfmr(277/480v) from the 3P 70A breaker.
I will run 4/c#250 from the secondary side 45kva xfrmr to a 225A MCB sub panel which will have 2P-125A breaker, (2) 2P 60 breakers. Can this suble panel be SINGLE PHASE? If so 3W?
I will run 1/0 aluminum SER cable from sub panel 125A breaker to trailer 125A breaker panel.
I will run #4 aluminum SER cable from sub panel 60A breakers to trailer 60A breaker panel. This is for 2 trailers.
Big question is if 3 phase 45KVA xfrmr will provide enough power for the (3) single phase trailer panels.
Thanks.
(1) w/ 125A MCB
(2) w/ 60A MCB
Thanks.