mhanson
- Redwood City, CA
- General Journeyman Electrician
Just looking for your thoughts on an Over Zellous Building Inspector.
Background: Just completed a Small Residential Service upgrade which included adding several new circuits to Bedrooms, Kitchen, Bath, Garage, etc... all new wiring meeting currents 2020 NEC code standards. during the project we decided with the homeowner, to replace the few remaining Knob and Tube circuits with modern Romex type wiring, this would eliminate all of the old Knob and Tube wiring.
When Inspector arrived for Final Inspection, He stated that since we rewired the entire home, we will need to make current the entire home, keep in mind this is NOT a home remodel and plaster walls are still intact, no added/removed walls etc... asking us to add several wall receptacles to meet the 6', 12' spacing rules.
Homeowner is quite upset as this will add several thousand dollars to her project, and I believe the inspector is over stepping.
appreciate your thoughts,
Thank You
Building Official is citing the following code sections:
California Electric Code 89.101.3:
The provisions of this code shall apply to the construction, alteration, movement, enlargement, replacement, repair of equipment, use and occupancy, location, maintenance, removal, and demolition of every building or structure or any appurtenances connected or attached to such buildings or structures throughout the State of California.
California Existing Building Code section 503.1
Alterations to any building or structure shall comply with the requirements of the California Building Code or California Residential Code, as applicable, for new construction. Alterations shall be such that the existing building or structure is not less complying with the provisions of the California Building Code or California Residential Code, as applicable than the existing building or structure was prior to the alteration.
Thank You