ptonsparky
Tom
- EC - retired
The face up rule was in 2020 and 2023 added a face down rule.I saw in 2023 they had to add a rule that panelboards can not be installed face up because apparently someone did that at a laundromat. There’s no rule against installing them face down though….. We can’t make enough NEC rules to stop stupid.
408.43 Panelboard Orientation.
Panelboards shall not be installed in the face-up or face-down position.
I agree to that.Working space?
Probably not applicable since no fuses or OCPD?
Working space has nothing to do with fuses or other types of OCPD. I require 110.26(A) for all disconnects as those are very likely to have the voltage checked while they are energized.Working space?
WA state has an amendment that disconnects without fuses or breakers doesn't need to comply with 110.26. They treat it like a single pole switch. So there are some places that view this as an important factor. I think that 3r isn't enough for a bellow grade install like that without a structure.Working space has nothing to do with fuses or other types of OCPD. I require 110.26(A) for all disconnects as those are very likely to have the voltage checked while they are energized.
CMP 11 addressed that issue for AC disconnects in the 2023 code.WA state has an amendment that disconnects without fuses or breakers doesn't need to comply with 110.26. They treat it like a single pole switch. So there are some places that view this as an important factor. I think that 3r isn't enough for a bellow grade install like that without a structure.
440.14 Location.
Disconnecting means shall be located within sight from, and readily accessible from, the air-conditioning or refrigerating equipment. The disconnecting means shall be permitted to be installed on or within the air-conditioning or refrigerating equipment. Disconnecting means shall meet the working space requirements of 110.26(A). ...
They'd still need to remove the amendment for it to not apply to other things like hot water heaters and disposals.CMP 11 addressed that issue for AC disconnects in the 2023 code.
Why do you heat hot water? My standard question every time I see "hot water heater".They'd still need to remove the amendment for it to not apply to other things like hot water heaters and disposals.
'Hot' is subjective.Why do you heat hot water? My standard question every time I see "hot water heater".![]()
Because I want my shower water hot, not just heated from 55°F to room temperature.Why do you heat hot water? My standard question every time I see "hot water heater".![]()
I've been guilty of pushing the 5°on lap siding but I've never done 90°Even if that were a NEMA 3R switch it would be against the installation instructions to install that way. They always say something like less than 5deg from vertical.