GarwoodV6
- Houston suburbs
- 30 year commercial Electrician
200A residential panel in garage for supplying ACCU's, 240V Appliances, pool, and a panel in the house to supply the gas furnace & all the other loads.
The house panel feeder is original #4SE aluminum cable. 310-15(b)ampacity chart lists
#4 AL rating at:
55A@60*C 65A@75*C.
I assume that going up 5A to the next size up OCP applies.
Can this feeder go on a 70A circuit breaker?
Or does the 60* rule apply for residential feeders <100A, forcing me to stay with a 60A CB?
I am not a fan of small aluminum wire but the homeowner doesn't want to replace the feeder.
#4 AL rating at:
55A@60*C 65A@75*C.