wondervamp
 - SF Bay Area
 - Shop technician
It is my understanding that you can hook up a single phase, 208 / 230V appliance to a 3 phase panel? The appliance is a RTU/Hvac compressor/condensor for a mini-split (heating/cooling) unit.
I think it's correct if I'm going for 240V, to connect between A phase and B phase. And if I have a lot of 120/240V loads on the panel, it will help phase balance to make one of the phases the wild leg (orange) (i.e. don't just pile everything onto the low phases A and B).
The 3 phase panel is: 3 phase, 240V Delta, High leg C - MY CONFUSION comes from determining which lugs in the panel are considered A, B, and C.