Nipple rule
This might be something then that needs either more attention or AHJs need an amendment for clarification or best option is everyone who matters and has read this thread should keep their mouths shut when training the next inspectors about this being a rule and then the status quo that you mentioned will be maintained longer.
The primary proposal to get rid of the rule was the from the IAEI.
PVC also requires first support to be within 36", so I feel it is fine with no additional supports as well for 36" and less runs.
Too flimsy for me, but then I think the only use for PVC is underground. Looks terrible in any above ground application unless you support it every 12" or so :D
Vertical installs tend to look alright. I've used 2 inch ta with a box adapter thats pvc often and that's not much room for a strap and is a good use of pvc for service equipment.
Most of the inspectors in WA are in IAEI so if that's what's pushed by them then they'll most likely turn a blind eye longer to these specific short nipple sections. If the organization was pushing for strapping it then they'd be inclined to flag this issue in their inspections since they'd be technically correct even if it's an impossibly short section of conduit even 1 or 2 inches.
Why not support the rule that removes the ambiguity and provides for no required to strap below a certain length? IMO The IAEI is another interest group that we could do without on the CMP's.
Separate issue but even without other organizations there will always be special interest involved with building codes. There's just too many factors involved. Otherwise we'd end up either with sysmic bracing in the midwest like in California or we'd have no standard wire colors. I'm all for it being actual electricians supporting their side of the code vs manufacturers and vendors.
Honestly I'm dumbfounded as to why they objected to having up to 18" of unsupported raceway. I can only believe that it has to do with the first part of the word dumbfounded. :unsure:
They don't think that the current rule requires that support and saw the 2008 rule as requiring supports that were not required in the previous codes. The IAEI and the CMP members do not actually understand what the code rule says.
Yeah I was reading over their proposal again and trying to figure it out. On one hand it seemed like they had good intentions and didn't want a new unnecessary rule - but they seem to want to go with the "that support isn't really enforced anyway" philosophy. I don't agree with that. I have added support to 12" nipples because you never know what kind of inspector you will get. And I work in many different unfamiliar jurisdictions.
They include specific wording that say up to 36" sections of raceway between two enclosures, boxes, etc. do not require support.
Can you post that reference? I am not aware of that specific wording
The easiest fix would be the proposal of mine that they rejected. It said where there is an unbroken length of raceway between two enclosures, the conduit terminations shall be permitted to secure and support the raceway. When I proposed it, it was in the form of an exception.
I am attempting to add 358.30(C) back with 24" instead of 18"
I thought they did support it's removal maybe I miss read this post.
IAEI wanted it removed because of the word "unbroken" in the language that would then drive the need for a strap on 2 9" sections of RMC.